Jay,

Divide inverter capacity by LVD then divide by full load efficiency. Example: 4000 Watt inverter shuts down at 42 volts, efficiency 85% = 4000/42 = 95A/.85 = 111 Amps. Then it depends on the insulation and conductor type and the corrections for ambient temp.

How can you not consider voltage drop? This is important for the surge capability of inverters. If the battery-inverter run is long you could have significant voltage drop for a wire correctly rated for ampacity.

Larry Crutcher
Starlight Solar Power Systems

On 1/1/15 7:23 PM, jay peltz wrote:
Happy new year all.

I have a question on wire sizing for the following.

250 amp breaker, in a UL enclosure ( say midnite or outback etc)
conduit from battery box to enclosure

I'm wondering how folks size this for ampacity not voltage drop.

thanks

jay

peltz power





_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to