I believe that that breaker is primarily used for the charging circuit of the 
SWs.I usually find this tripped during the charge cycle. I would verify; when 
the breaker trips, check the charge settings menu10 + the AC2 input settings, 
also check that you don't have a bad battery causing over charging. Let me know 
off list as I have in my truck a 30A breaker that I use as a replacement for 
the SWs.Tump
On Jan 21, 2015, at 10:02 PM, Allan Sindelar wrote:

> Two relevant details of note here:
> 1. The breaker on only the 5548 model was of a "toggle switch" configuration, 
> rather than the push button used on the rest of the models. If you have a 
> push button as you describe, the problem may be that it was an incorrect 
> previous replacement.
> 2. As Ray has noted, the 4048 could out surge the 5548. They had different 
> firmware, giving the 5548 a tighter voltage window during surges, resulting 
> in less surge capacity due to less tolerance for voltage dips under surge 
> loads.
> Allan
> 
> Allan Sindelar
> [email protected]
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
>  
> On 1/21/2015 7:38 PM, Ray Walters wrote:
>> Try Mouser electronics.  Otherwise, I'd consider bypassing it, and have a 
>> regular breaker (30 or 40 amp) on theout put. 
>> The tripping was probably because the breaker was malfunctioning. Usually 
>> the SWs will trip their on board computer to shutdown for over current, and 
>> the breaker should never be used. The 5548s were kind of weird though.  I 
>> never liked those.  I've had SW4048s out surge the 5548s hands down.
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer, 
>> Licensed Master Electrician
>> Solar Design Engineer
>> 303 505-8760
>> On 1/21/2015 12:24 PM, [email protected] wrote:
>>> Hi all- 
>>> I'm having some difficulty finding a replacement for the little push-button 
>>> circuit breaker on an old Trace SW5548 inverter. This is located on the 
>>> lower left corner of the box, below the wiring access panel. The customer 
>>> has had             repeated tripping of this breaker from overcurrent, so 
>>> it has been doing it's job. But now the button won't reset.
>>> It's a 35 amp breaker.  I have only been able to find smaller ones in the 
>>> online catalogs.
>>> Anyone know of a better parts supplier?
>>> Thanks
>>> Don Barch
>>> Energy Solar
>>> 
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected]
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> [email protected]               www.SWNL.net
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to