Looks like they use 24VDC for contactor activation, not 120VAC.
*From:*RE-wrenches [mailto:[email protected]]
*On Behalf Of *Mark Frye
*Sent:* Monday, February 02, 2015 1:29 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Rapid Shut Down and the 10 Second Rule
Questions
OK. So did you run a line 120V up to the box on the roof to energize
the coil of the relay up there?
Mark Frye
On 2/2/2015 9:13 AM, Jerry Shafer wrote:
The units we have used have a large contactor inside the combiner
box made by AMtec Solar. this was required to control the shut
down includes a fire button done on the ground floor
Jerry
On Mon, Feb 2, 2015 at 5:49 AM, Mark Frye
<[email protected] <mailto:[email protected]>> wrote:
Jerry,
What unit did you use?
Mark Frye
On 2/2/2015 7:43 AM, Jerry Shafer wrote:
Wrenches
We have installed some of these rapid shut down units and
they are always located close to the array and ours kill the
DC instantly as long as the inverter was running when this
accures did not test it with inverters already off.
Jerry
On Feb 2, 2015 5:34 AM, "Christopher Warfel"
<[email protected]
<mailto:[email protected]>> wrote:
We have a interpretation problem among some people I work
with with, and 690.12 Rapid Shut Down and the the 10 second
time for reducing ac and dc conductors to 240ma, and 30V.
The word "initiation" seems to indicate that all affected
conductors need to be at these levels within 10 seconds of
de-energizing either the ac or dc conductors. If so, then the
disconnects need to be co-located to meet this requirement if
this interpretation is correct.
I have read Mr. Brook's article in Solar Pro, but AHJs may
feel differently.
Would anyone care to weigh in on their interpretation?
Thank you, Chris
--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978 <tel:401-466-8978>
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org