Mac:

Apparently so, but this operation is not supported. It supposedly works. 

William



> On Feb 12, 2015, at 3:18 PM, Mac Lewis <[email protected]> wrote:
> 
> Hi Jay & William,
> 
> Just so I understand, you can put the mate into auto right after the eq is 
> enabled (not after eq has finished), and it will manage the generator?  Is 
> that right?
> 
> Thanks
> 
>> On Thu, Feb 12, 2015 at 10:45 AM, jay peltz <[email protected]> wrote:
>> I"ve had clients do it for years with no problems that I know of.
>> 
>> jay
>> 
>> peltz power
>> 
>> 
>> 
>>> On Feb 12, 2015, at 9:47 AM, <[email protected]> wrote:
>>> 
>>> Friends:
>>>  
>>> I understood the generator had to be started and stopped manually.  I have 
>>> a client who was using the sequence below to stop the generator 
>>> automatically.  To have the generator stop automatically has a convenience 
>>> factor, but I do like my clients to verify the cycle has accomplished the 
>>> prescribed regimen, and walking away from the process does not accomplish 
>>> that. 
>>>  
>>> I spoke with Outback regarding the procedure of engaging the auto mode 
>>> prior to completion of the EQ and the reply was that the system had not 
>>> been engineered to operate this way so the results could not be guaranteed.
>>>  
>>>  
>>> William
>>>  
>>> From: RE-wrenches [mailto:[email protected]] On 
>>> Behalf Of jay peltz
>>> Sent: Thursday, February 12, 2015 8:54 AM
>>> To: RE-wrenches
>>> Subject: Re: [RE-wrenches] Outback AGS & eq
>>>  
>>> Hi Mac
>>>  
>>> I don't think there is a global eq function. 
>>> Eq continues to be manual on inverters. 
>>>  
>>> Gen to manual on
>>> Initiate EQ 
>>> Gen to auto
>>> Done
>>>  
>>>  
>>> Jay
>>> Peltz power. 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> 
> 
> 
> -- 
> 
> 
> 
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to