Hi Kevin; I have both a comment and a question:
Comment) I thought that while charging, the AC loads were simply powered directly by the generator, and the inverters were operating strictly as chargers. My experience is that it is almost always an issue of poor waveform regulation with the generator. This is easy to check with a Fluke 87 or 89. Set to quick peak capture, and see what the peak of the waveform is. A clean sine wave of 120 vac will have a peak that is 1.41 times the RMS, or 169 vac. I've seen them as low as 135, or alternatively have weird spikes into the 200s.
Of course a scope reading is better, but not everyone can afford those. Question) Which inverter did you switch to that cured the problem? Thanks, R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 3/18/2015 9:20 PM, Kevin Pegg wrote:
This sounds like the exact same issue with the FX and VFX inverters. Meter the power quality while under charge - nasty. We found a lot of computerized control systems on furnaces and boilers would either reject the power and not power up, or would behave erratically, some would be ok if you powered it up before generator on, some not. They were fine on inverter, fine on generator, but under charge bad. Ended up swapping out a lot of inverters since customers were not so keen on certain loads not operating properly when under generator charge. Kevin -----Original Message----- From: RE-wrenches [mailto:[email protected]]On Behalf Of jay peltz Sent: March 18, 2015 5:32 PM To: RE-wrenches Subject: [RE-wrenches] outback radian question HI All, My question is. are there any known issues with the Radian interfacing with a generator? I have a customer with flickering lights. The lights are LED ( some dimmer/some on/off) The generator supplier says that there are lots of problems with the Radian. I've not heard this and don't believe it. symptoms: radian alone: no flicker generator alone: no flicker generator/charging flicker. different generator: no flicker. So there is no doubt its the generator. I'm trying to get more information to go back to the customer. Thanks jay peltz power _______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org