Thanks Jay. My preferred method and most economical as well as no cost was also
mentioned by you I was just asking if anyone can fault it - "8. Other option.
You can run the CC set points 5v above what you want and then run AUX 2 5v
below ( or what you actually want) and then connect the AUX 2 to the dump load.
So it'll dump as the bulk/absorb/float. So the CC will never disconnect, but
the diversion load will act like it is". This gives me full charge regulation
while the CC is ALWAYS charging with the AUX doing the actual regulation. I'll
stick in a time delay to minimize rapid cycling and we're good to go. I would
have approached this design very differently had I known that the Classic would
not actually protect the turbine from freewheeling w/o a $1000+ add on. I
probably would have gone with 48V transmission and spent the money or highly
reliable wire instead. However, the more I think about this AUX control method
the better it is sounding as it allows high V transmission.
>From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative
>SOLutions
____________________________________________________________
Old School Yearbook Pics
View Class Yearbooks Online Free. Search by School & Year. Look Now!
http://thirdpartyoffers.juno.com/TGL3131/550c4b8ccd8834b8c07e6st04vuc
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org