Hi Bill;

If the battery is in an insulated box indoors, it definitely can over heat. Also if ambient temps get into the 90s, the additional heat from charging can push the battery into the danger zone. In hot desert or tropical climates, it may actually be difficult to keep the battery below 105F. I'm very glad to hear Midnite added the high temp disconnect to their system. They may have saved a life. Bob, is battery temp logged, so we could see how often a system quits charging for high temp, and just what the battery temps are running? Many of our systems may need additional cooling. A recent HUP install in Haiti comes to mind.....

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 5/22/2015 8:28 AM, frenergy wrote:
Hey Jay,
From what I've heard form battery manus, the C rates likely even in a well PV-ed system still will not produce C-rates high enough to approach a high or "longevity reducing" internal battery temp, assuming a typical bulk, absorb, float cycle. Of course, battery environmental location (typical temps) would set a baseline from which batt temp would rise from. Here in the Sierra, ambients are not very high 95% of the time. Just curious, how does the wiz bang account for all loads...2 shunts?
Thanks,
Bill
Feather River Solar Electric

    ----- Original Message -----
    *From:* jay peltz <mailto:[email protected]>
    *To:* RE-wrenches <mailto:[email protected]>
    *Sent:* Thursday, May 21, 2015 8:07 PM
    *Subject:* Re: [RE-wrenches] FLA battery setpoints with larger arrays

    Hi Allan,

    I like the classic/wiz bang jr.  This allows really good end amp
    control as all loads are accounted for.

    Higher C rates equal higher internal temps which definitely will
    shorten the life.

    On Thu, May 21, 2015 at 10:56 AM, Allan Sindelar
    <[email protected] <mailto:[email protected]>> wrote:

        Wrenches,
        In the last few years I have changed my approach to off grid
        system sizing, primarily due to higher battery costs and lower
        module costs. Rather than shooting for a traditional 80-90% of
        winter load profile target, I will size a larger array and
        smaller battery bank, figuring (especially here in the sunny
        Southwest) that batteries will recharge more quickly, will
        spend more of their time full (and thus last longer), and will
        be at least partially charged during cloudy weather. This even
        allows for smaller battery banks that are cycled more deeply
        (as long as there's a backup gennie in the mix); the lower
        cost of a smaller size may allow for a set of higher-quality
        industrial cells.

        I first began to rethink my design approach after reading
        Christopher Freitas' Solar Pro article on large battery banks
        a few years ago. Being able to refill in a day was part of his
        strategic approach to battery bank design. I used and wrote
        about this approach in my tiny house article in the current
        Home Power. However, I'm just beginning to get owner feedback
        about greater water consumption and the need for more frequent
        watering. This is especially the case when I add array to an
        existing system, and the old watering schedule is suddenly not
        enough.

        When I design new systems I now encourage larger arrays and
        smaller battery banks, as the batteries spend more of their
        time happily full and recover more quickly after a discharge
        period. But I am thinking that I will have to begin changing
        charging setpoints in response. Flooded batteries have a range
        of recommended bulk setpoints, from 28.8 to 29.6 volts on a
        24V system. When arrays were smaller we set to the higher end
        of the range to take advantage of topping off when available,
        and a two hour or longer absorption was considered beneficial,
        as long as the CC could transition to float at 2% of capacity
        or so. With a larger array a better approach may be to lower
        the bulk/absorption setting, as well as reduce absorption time
        and raise the float transition current ("done amps").

        I'm writing to encourage a discussion among off grid Wrenches.
        Are you changing the relative relationship between array and
        battery capacities? If so, how are you adjusting charge
        controller setpoint programming? For example, how would you
        program a Midnite Classic, Outback FM or Schneider XW if you
        could achieve a C/10 or C/15 charge rate?

        Thanks, Allan

        *Allan Sindelar*
        [email protected] <mailto:[email protected]>
        NABCEP Certified PV Installation Professional
        NABCEP Certified Technical Sales Professional
        New Mexico EE98J Journeyman Electrician
        Founder (Retired), Positive Energy, Inc.
        *505 780-2738 <tel:505%20780-2738> cell*



-- Jay Peltz
    Peltz Power
    [email protected] <mailto:[email protected]>

    ------------------------------------------------------------------------
    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to