On 5/23/2015 11:37 AM, Luke Christy wrote:
Jay's point about adding PV to offset daytime AC for the battery bank brings up 
the issue of active cooling.

How many folks out there are installing some form of cooling for LA battery 
banks, and how are you implementing it?


As long as some FLA battery systems use "vent fans", just arrange them so
that they move air past the batteries to cool them at the same time ?
That's when they're going to get hottest anyway.

FLA batteries will freeze easier if they are discharged. I suppose that you could
use the battery temp sensor to make sure you charge them up good when
the temp gets cold enough.

boB




The issue of excess heat being an enemy of battery life has had me concerned 
for several years now, and I have started installing multiple fans in battery 
boxes to increase the cooling from air circulation, but I'm not sure I have the 
effectiveness dialed yet.

Interested to hear what others are doing here.

As always, I appreciate the great resource that is this list.

-Luke



Message: 2
Date: Fri, 22 May 2015 17:07:05 -0700
From: jay peltz <[email protected]>
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] FLA battery setpoints with larger arrays
Message-ID:
        <CAGr8+7chy-FBp8yzQbNp4T7+wKLyE2LjJ6zy97w=6dqjhkt...@mail.gmail.com>
Content-Type: text/plain; charset="utf-8"

Hi Ray,

Cold isn't a problem.  It reduces capacity and yes they could freeze, but
it doesn't shorten life ( I mean besides the freezing part) in fact cooler
batteries last longer.
But hot is a problem. Those max temps are not the same thing as reduced
life from running at a hotter temperature.


As to internal temps, its really hard to do this.  IR cameras are pretty
good.  Temp sensors which stick to the outside of the case's are not as
good as ones that bolt to the post.  The post is a good thermal conductor
vs the plastic case.  The glue/stick on ones come loose as we all know and
that means less accurate metering.

My premise for bring up the temp concern is that with a larger array and
smaller battery which equals higher C rates you will have higher internal
temps, no way around it.  How high, how much/will it shorten the life
unclear but probably, how much, ?

Let me rephrase it, do you think hotter temperatures are increasing the
lifespan of the battery?

While on this subject, I've done some quick calcs and with hot areas, its
cheaper to add PV for installing daytime AC vs battery life lost due to the
heat.  We can thank the cheap world of PV for that.

And while I've thought about what Allan started this conversion with in
regards to sizing batteries.
I continue to size my batteries around best life for the battery  ( best
daily average % DOD).
There are many ways to consider the size/cost etc of batteries:  For a
larger battery (less DOD)  you could view it as buying lead futures, longer
time between problems, etc.  For smaller bank ( higher DOD)  my only reason
for doing it at this point is a bridge battery to when Li-Ion/other
technologies will overtake LA for cost/ease/MX/capabilities.

I'd be curious to hear what others think about that last part,

jay




Luke Christy

NABCEP Certified PV Installation Professionalâ„¢: Certification #031409-25
NABCEP Certified Solar Heating Installerâ„¢: Certification #ST032611-03
CoSEIA Certified PV Installer

Solar Gain Services, LLC
PO Box 531
Monte Vista, CO. 81144
[email protected]
719.588.3044
www.sgsrenewables.com

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to