Jay,
Whoa, I'd be careful there. Unless there's been a change while I was
away on my bicycle, Outbacks are still 140V rated maximum voltage
and 150V hard maximum. 142Voc in May suggests that doubling strings
in series will easily exceed max Voc in winter. That's why I
previously suggested Classic 200 or 250. Am I missing something?
Allan
Allan Sindelar
[email protected]
NABCEP Certified PV
Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive
Energy,
Inc.
505 780-2738 cell
On 5/31/2015 2:23 PM, jay peltz wrote:
HI Luke,
To add here. I'm unclear if you have measured each string
or the whole array at 71v.
I would check each string for voc/isc.
And then if they are consistent, I agree that putting 2
strings in series with a new controller might help out.
You can try it with the MX-60 as you are at only 142v. If
it works better then a new higher voltage CC would be required
for winter higher voc.
Let us know what you find out.
jay
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
|
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org