One of our local utilities just denied the use of the ConnectDER... some
nonsense about excess weight if the customer also has a surge suppressor
and generator input collar device already. They just blanket prohibited it
even for customers that have no existing collar devices installed.

#smallminds

Jason Szumlanski
Florida Solar Design Group



On Mon, May 25, 2015 at 7:58 PM, <[email protected]> wrote:

> wow, engenius. thanks for posting this.
>
>
>
> http://connectder.com/products
>
>
>
> todd
>
>
>
>
>
>
>
>
>
> On Monday, May 25, 2015 4:48pm, "John Blittersdorf" <
> [email protected]> said:
>
>  Bill,
>    One clean way to do it would be to use a ConnectDER, but the max input
> is 11.5 kw.  We have used several of these for under 10 k installations and
> have saved lots of install time.   They are not cheap (approx $300+).  Our
> power company sells them to installers.
> John Blittersdorf
> Central Vermont Solar & Wind
>
> On Mon, May 25, 2015 at 12:39 AM, frenergy <[email protected]> wrote:
>
>>  Wrenches,
>>
>>         Customer currently has a hacked up 200 amp Sylvania meter/mains
>> panel.  He also is averaging a load of 74 KWhrs/day! which will require
>> about 15  KW system size at this site.  Obviously a system this size cannot
>> backfeed the busses in the load center.  Because the exiting panel is a
>> mess anyway, I'm suggesting it gets changed out.
>>
>>         What sort of new 200 amp service would facilitate a clean supply
>> side connection.  One thought is have separate Utility meter socket then a
>> 12 X 12 J-box with a monster power distribution block in it and then a
>> distribution panel (without the meter socket)...this being a way to insert
>> a means to grid-tie between the meter and the 200 amp main breaker.  A
>> little spendy but nothing like going to higher amp service to be able to
>> load side connect.
>>
>>         A 400 amp panel is not an option as the existing 165' of 3" pvc
>> underground conduit to the pole currently has 4/0 alum.  The utility says
>> it would have to be 4" for the new cable and the cost $10K+ for the upgrade.
>>
>>         Other ideas??
>>
>> Thanks in advance
>>
>> Bill
>>
>> Feather River Solar Electric
>>
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to