Gennys and battery settings are all good but if the battery died in the
genny or its out of fuel then all bets are off so things happen more often
then you might think. Backing up is insurance, like I said there are other
options out there.
Jerry
On Jun 6, 2015 10:54 AM, "Jeff Clearwater" <[email protected]>
wrote:

> Hi Mark
>
> Set up properly with the 3 protection thresholds  plus generator auto
> start you shouldn't need any DC PV input.  Seems a shame to spend the money
> on a charge control etc when SMA has carefully provided a built in
> solution.
>
> If you do decide to go that route you'll need to install a Shunt and set
> up the DC Current Sense circuit so the inverter knows what other current is
> flowing to and fro the batteries.
>
> Best,
>
> Jeff
>
>
>
>
>
> Sent from my iPhone
>
> On Jun 6, 2015, at 7:23 AM, Mac Lewis <[email protected]> wrote:
>
> Hi Mark,
>
> The Sunny Island has various battery protection modes and will shutdown
> based on user programmable state of charge levels. Level 2 battery
> protection will start the Sunny Island every 2 hours in an attempt to get
> charge into the batteries.  You should set this level up at times when
> energy input is likely.  See page 113-114 here:
> http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-20.pdf  If it doesn't
> get any charging to the batteries for 10 minutes, it will shut down and
> wait again.
>
> This is an advantage of having at least some DC coupled solar input.
>
>
>
> On Sat, Jun 6, 2015 at 7:39 AM, Mark Frye <[email protected]> wrote:
>
>> Hi Guys,
>>
>> Just wondering about how a SI/SB microgrid works. If all the PV is
>> connected to SB inverters, what happens if the loads manage to drain the
>> batteries to their low voltage shutdown? Wouldn't the SB stop providing the
>> AC sync so then the SB wouldn't have anything to sync to even if they had
>> power available from the PV?
>>
>> How is this handled? It seems to me you would always want to have some
>> amount of PV DC coupled.
>>
>> Thanks,
>>
>> Mark Frye
>> Berkeley Solar Electric Systems
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to