Have you performed insulation resistance tests on the DC conductors (megger)?

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.

-----Original Message-----
From: "Howard  Scot  Arey" <[email protected]>
Sent: ‎6/‎18/‎2015 8:30
To: "[email protected]" <[email protected]>
Subject: [RE-wrenches] Repetitive and unknown arc-fault codes with this 
combination...Sunpreme bi-facial and Fronius IG

I need some help please!  I'm quickly losing credibility with two of my
customers.

 

We have two installations with Sunpreme GxB 350 bi-facial modules and
Fronius IG inverters.  They keep throwing Error code 240 - arc fault on the
Fronius IG.  

 

We've been up and down these installation three times checking connections,
replacing connectors, tightening connections, checking for chafed wires.
Nothing to cause any visible angst.

 

The team here is wondering is perhaps the module itself might be the source
of the problem, with some DC arcing inside the J-Box.  Any thoughts?  We
can't open the j-box on an broken module (be careful handling frameless
glass on glass modules :)) because there doesn't appear to anything
accessible with modern potted j-boxes.

 

As for the conditions when we get these arc fault codes - typically the peak
of a sunny day when they're making max power.

 

Each of the installations is a bit different. On the 7KW install with
Fronius 7.5, we've run the two strings (10 modules each) back to the
inverter separately.  On the 10.5KW install with the Fronius 10.0, we ran 3
strings of 10 to a combiner box, then one set of conductor back to the
Fronius 10.0 where we used the distribution plate to spead the amperage
across the six string input channels.

 

I'm stuck - any thoughts on other potential arc-fault causes?

 

Howard "Scot" Arey

254-300-1228

[email protected] <mailto:[email protected]> 

 



 



[The entire original message is not included.]
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to