Hey Al,

 

I had a similar choice to make several months ago.  There are not that many 
options out here in Hawaii—given the more demanding utility requirements for 
grid-tie inverters—for string inverters that are true 3-phase 120/208 while the 
choices are more abundant if you have 277/480 as the service voltage.  The 
Fronius Symo has a 12 kW @ 120/208 model which I plan to use soon.

 

For this last ~ 100 kW system we did, we used five SMA Tripowers and a 
step-down x-former to bring the voltage down to 120/208.  As for transformers, 
note that Dongan (made in the U.S.) offers such high-efficiency x-formers even 
in stainless steel enclosures at a very reasonable price.  Given the 1,000V DC 
max input possible for the Tripowers, we went into unknown territory with the 
AHJ here on the Big Island.  While I spec’ed out 1 kV-rated conductors for the 
+ and – DC conductors, I realized late in the game that I needed to use 1 
kV-rated EGC wire from the roof as well.  D’oh!  Trying finding some of that at 
your local electrical supply.  Finally, to my surprise and somewhat annoyance, 
we are being required to erect a protective barrier, i.e., fence, around the 
inverters—which are mounted on the exterior wall of a medical professional 
building—in order to keep them beyond the reach of the public, even though one 
would have to take covers off in order to expose the conductors.

 

Always an adventure.

 

marco

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Jason Szumlanski
Sent: Friday, June 26, 2015 9:39 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] central vrs string inverters

 

I don't have anything in terms of advice on the Tri-Power, but I have done 
microinverters on straight 208V three-phase and also 480V with a step-down 
transformer. While there are more potential points of failure, future service 
is straightforward. There are lots of capable people who can swap a micro. We 
have been called out to several 20-100kW central inverters that were 
essentially unserviceable due to obsolescence, bankruptcy, parts availability, 
and lack of qualified personnel. That could be a function of the crummy Florida 
commercial solar market, but it's something to consider. Lifetime service and 
replacement costs need to be considered in the ROI analysis, and despite 
micro's higher initial cost, there is a good argument to be made...

 

On the other hand, while I have never used a Tri-Power, SMA's Sunny Boy's have 
been rock solid around here in demanding conditions.

 

Jason Szumlanski


 

 

On Fri, Jun 26, 2015 at 9:26 AM, Allen Frishman <[email protected]> wrote:

Hi Wrenchers,

I am considering using 8 SMA Tri-power Inverters for a project with a 3 phase 
208V Grid which means I have to add a step down transformer (480V to 208V).    
I am comparing this option to a central inverter.    I have done many of the 
central inverter systems at the 208V but have yet to try the 20+ KW string 
inverters with the addition of a step down transformer.

 

I know that both systems have there own pros and cons and I will really 
appreciate some feedback from those that have experience doing both types.   

 

For the central inverter there are fewer inverters to malfunction however when 
one does the entire system is down.   In my experience the Central Inverters 
that I have used have been very reliable.       

- Anyone seeing reliability issues with the SMA Tri-power 20KW and 24KW string 
inverters?

 

Note:   My project is under NEC 2008.

 

All feedback is appreciated.

 

Al Frishman
AeonSolar

(917) 699-6641 <tel:%28917%29%20699-6641>  - cell
(888) 460-2867 <tel:%28888%29%20460-2867> 
www.aeonsolar.com <http://www.aeonsolar.com/> 

 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to