Hi:

Copper conduction losses are proportional to (current) x (current) x 
(resistance).  For the same wire gauge, double the current means that the 
losses increase by 4X.

Going from 150 VDC to 300 VDC will therefore allow you use 4X thinner wire 
and going up to 600 VDC will allow you to use 16X thinner wire.

It's very non-linear.

JARMO
_____________________________________________________________________________________
 


Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  | 
  Sales Application Engineer 
Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
+604-505-0291 
Email: [email protected]  |   Site: www.Xantrex.com 
|   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 








*** Please consider the environment before printing this e-mail




From:
Jerry Shafer <[email protected]>
To:
RE-wrenches <[email protected]>, 
Date:
07/22/2015 11:52 AM
Subject:
[RE-wrenches] DC conductor line loss numbers
Sent by:
"RE-wrenches" <[email protected]>



Wrenches
Some time back there was discussion on the conductor size and efficiency 
rating requirement for long DC runs.
What I am looking at is this, 400 feet of MCM 400 to keep the line loss at 
or below 1% per NEC code for an off grid application, cost vs return is 
not acceptable. 2/0 is less than 2.5% and the cost is far less. Specs are 
4 strings of 3, 250 watt modules feeding one Outback FM 80 charge 
controller. There are lots of things I can do like SMA instread, or 200 
VDC charge controller but nothing can be changed except the wire gauge. 
Does anyone recall a thread with this topic.

thoughts ??
Jerry

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to