Howie,
If meggering an array, first of all, check with your panel oem to see what 
voltage they recommend to safely IRT. In a series string, you are effectively 
meggering at the meter voltage plus the cumulative series string voltage. If 
the meter is set to 500v, and you are measuring a string which is 500 vdc open 
circuit, the last panel in the string is meggered at 1000v, the middle panel 
750v, etc.

Kirk Herander
VSE
Sent from a job site somewhere 

> On Jul 23, 2015, at 8:18 AM, Howie Michaelson <[email protected]> wrote:
> 
> We are starting to work with 1000 volt arrays.  What different settings
> should we be using for testing insulation on these array?  Anyone have a
> favorite megger for testing these arrays.
> 
> Thanks as always,
> Howie
> -- 
> Howie Michaelson
> NABCEP Certified PV Installation Professionalâ„¢
> Catamount Solar, LLC
> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to