August:

 

I know conduit and boxes seem way too hard for the new generation of 
plug-and-play installers.  Because of this we’ve seen a trend to cheapen how we 
run DC circuits.  We can’t let this dissuade us from doing our jobs safely and 
correctly. 

 

If this question were asked about any other kind of power circuit, Journeymen 
and women would shake their heads wondering why the fuss about a little bit of 
EMT work.  Power circuits, DC or AC, deserve to be protected in conduit, cable 
tray or other approved methods, and those methods have long been established.  
I don’t imagine you could install rooftop air conditioner feeders by 
cable-tying them along strut or conduit.  Why is it that PV installers figure 
this is OK for 600 volt DC circuits?

 

I think it is bad enough that high voltage DC circuits are allowed to be 
unprotected under arrays, but once the circuit leaves the perimeter of the 
array there is no excuse to leave the conductors vulnerable to damage and to 
hurt people.

 

The problem is that, although you are ethical enough to weigh the long term 
implications of various solutions, many installers and inspectors are not.  
Many then get away with or approve of tying high voltage cables to whatever is 
handy. You and I cannot therefore do a safe job and provide bids that are 
competitive in price.

 

Sorry if I appear to have a strong opinion on this subject, but poor electrical 
practices do kill people, and I take that seriously.

 

Sincerely,

 

William Miller

 

 

 

Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/> 
805-438-5600

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of August Goers
Sent: Tuesday, August 11, 2015 3:20 PM
To: RE-wrenches
Subject: [RE-wrenches] wiring methods between arrays

 

Hi Wrenches,

 

I have another best practices questions: what are you doing to run your PV wire 
between arrays on a rooftops? This question has come up on this list in the 
past but I’m still on the hunt for a robust and faster lower cost method. We 
mostly install outdoor boxes on each sub array and then run EMT between these 
boxes. We use strain reliefs to enter the boxes and then either keep PV wire or 
transition to THWN-2 in the EMT depending on the layout.  This method takes 
time and the outdoor boxes aren’t cheap. Alternatively, we can run open-ended 
EMT with ground bushings on the ends to bond the conduit. Since ground bushings 
are designed to be used in boxes we switch out the aluminum lug with a 
tin-coated outdoor rated lug and stainless hardware. This technically violates 
the listing but at least the materials hold up. The EMT needs to be carefully 
bent down at the ends so rain doesn’t enter. Lastly, we sometimes run our PV 
wires along strut or angle aluminum (this is the fastest method) which also 
needs to be bonded with a lay-in lug. 

 

Does anyone have other methods?

 

Best,

 

August

Luminalt

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to