We actually planned on bringing that to him next time as well, he didn’t care 
that we said we would be tied off if any work were needed in the future, but 
the words “permanently installed” might change his tune. 

 

With Regards,

 

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of [email protected]
Sent: Thursday, August 13, 2015 10:38 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Serviceable equipment on a roof

 

Daniel:

 

Could you install permanent fall protection anchors strategically located?  
Service personnel could anchor in wherever needed. S-5 style fall anchors are 
made. 

 

Wm




On Aug 13, 2015, at 7:30 AM, Daniel Young <[email protected]> wrote:

We have a job going in on  1 ¼”:12 standing seam commercial roof. When we tried 
to walk the drawings through the permit department, we were told that we had to 
keep the solar modules 10’ from the roof edge because they are serviceable 
equipment.

 

We’ve run into this before, and have been successful arguing that the solar 
modules are not installed as serviceable equipment (they require service 
intervals closer to the roof membrane on flat roofs [little to no attention for 
20+yrs], rather than the roof top AC unit as an example). We install all 
pass-thru boxes or other similar enclosures at least 10’ from the roof edge as 
well to make it clear the most likely parts to be inspected/serviced would be 
safe. We also pointed out the International Fire codes rules on keeping the 
array 4’ from the edge of the roof (smaller commercial building, so we are in 
the 4’ setback category, rather than the 6’ setback). To all this he said “you 
can’t tell me that no one will ever service those solar modules. If someone 
falls off the roof and dies, I wanna be able to say I did my job…”

 

So, I think my only option is to point to a well backed definition for 
serviceable equipment to show him that the solar modules do not qualify. Does 
anyone have any good source to help with this issue? Or would the majority of 
you say that 10’ is the right call anyway?

 

I know I might just be up against a hard ^%$# inspector and have to just go 
with it, but I also do not want to set precedent within my states default 
commercial code agency if I don’t have to.

 

With Regards,

 

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6086 / Virus Database: 4392/10423 - Release Date: 08/12/15

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to