HI Drake,

What sort of multi stage relay control are you using?

jay
peltz power


> On Aug 21, 2015, at 5:27 AM, Drake <[email protected]> 
> wrote:
> 
> I'm considering an AC coupled system with Enphase that would shed inverters a 
> group at a time, ending up with one still charging until the set point is 
> reached. 
> 
> At 12:56 AM 8/21/2015, you wrote:
>> Hi Folks;
>> 
>> I've done more research on the whole AC coupled issue, and one flaw I found 
>> with both the Sunny Island and the Radian is that they can't really do a 
>> full 3 stage charge for the batteries in off grid mode.
>> They detect that the batteries are full and disconnect the AC coupled GT 
>> inverters, but this is about as subtle as the very early charge controllers, 
>> and amounts to 1 stage charging.  This is fine for temporary outages, and 
>> when the grid comes back, the batteries get a good 3 stage charge.  But 
>> these folks are really wanting a design that could be taken off grid 
>> permanently.   Also as you my recall, the GT PV system is Enphase, so we 
>> can't use the more sophisticated controls that SMA offers for the Sunny 
>> boys. 
>> I hate to say it, but I might be back to a diversion load with PWM 
>> controller.  Not elegant, but we could get 3 stage charging.  
>> Every time I look at AC coupled setups, I just want to start over with 
>> charge controllers. 
>> 
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer, 
>> Licensed Master Electrician
>> Solar Design Engineer
>> 303 505-8760
>> On 8/17/2015 9:39 PM, Mac Lewis wrote:
>>> Hi Ray, 
>>> 
>>> With that size grid-tied system, you would want to use a battery based 
>>> inverter(s) near the (6.7/0.8) 8000W range.  
>>> 
>>> The frequency shift of the Sunny Islands will work with kicking out the 
>>> enphase inverters but you wouldn't get the same output ramping that it 
>>> would offer if it was a Sunny Boy grid-tied inverter.  The Sunny Island can 
>>> effectively solve your generator backfeeding because there is a reverse 
>>> current sensor that will disconnect the AC input at whatever level you 
>>> want, 50 mA is default I think.  You may need to give the Sunny Island 
>>> generator start control for this however.
>>> 
>>> You can read about it here on page 137.
>>> 
>>> http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf 
>>> <http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf>
>>> 
>>> You'll need to give the Sunny Island a digital signal that tell it whether 
>>> its connected to a generator or a grid as outlined in the manual. 
>>> 
>>>  This is where the Radian is nice because it has two AC Input terminals.
>>> 
>>> Sounds like an interesting project.
>>> 
>>> Good Luck.
>>> 
>>> 
>>> 
>>> 
>>> On Mon, Aug 17, 2015 at 8:36 PM, Jerry Shafer <[email protected] 
>>> <mailto:[email protected]> > wrote:
>>> 
>>> I cant see this working well without some battery based inverter
>>> Jerry
>>> On Aug 17, 2015 10:10 AM, "Ray Walters" <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>> HI Esteemed Wrenches:
>>> 
>>> I am consulting on a system I have never seen, that consists of a 6.7Kw 
>>> Enphase roof mounted system, and 2 backup generators.  Each generator has 
>>> an automatic 200 amp transfer switch to back up its own 200 amp panel.  
>>> Both 200 amp panels are fed by a 400 amp service from the grid.
>>> The Enphase PV backfeeds a subpanel in another building which then is fed 
>>> by a 2 pole 60 amp breaker in one of the 200 amp panels.
>>> Currently they are having issues with the generators kicking out because of 
>>> the Enphase inverters.  That part I understand: you can't backfeed a 
>>> generator, or its voltage regulation freaks out.
>>> 
>>> Now we get to the fun part: they want to create a third critical load 
>>> subpanel with loads selected from both 200 amp panels to be powered by 
>>> batteries and an inverter.
>>> I am considering the Sunny Island since it makes the most sense with its 
>>> ability to signal the Enphase inverters to shut off when the batteries are 
>>> full.  I also see this as a partial solution to the generator issue, since 
>>> normally the Enphase will be connected to the output side of the Sunny 
>>> Island.  However, when the generator is used to charge, we will be back to 
>>> directly coupling the generator output to the Enphase.
>>> 
>>> Here are some possible solutions I'm considering:
>>> 1) Use a separate charger for the generator so that it will only feed DC to 
>>> the batteries, and not be AC coupled.
>>> 2) convert the PV back to DC with charge controllers, but that would 
>>> involve ditching and adding another conduit run between buildings.
>>> 3)  Put the Enphase PV on a relay that would disconnect the PV when 
>>> charging with the generator.
>>> 4) Something I haven't thought of that one of you clever folks can 
>>> suggest......
>>> 
>>> As always, thanks in advance for all you responses,
>>> 
>>> -- 
>>> R.Ray Walters
>>> CTO, Solarray, Inc
>>> Nabcep Certified PV Installer,
>>> Licensed Master Electrician
>>> Solar Design Engineer
>>> 303 505-8760 <tel:303%20505-8760>
>>> 
>>> ______
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to