Brian,


I don’t know that I have a lot of good news for you. I have looked into this 
and I really don’t see a good way out of making some pretty conservative 
assumptions. You can read what I wrote in my IAEI article on Support of Exposed 
Cable earlier this year. I get into ampacity briefly though it is not the focus 
of the article.



http://iaeimagazine.org/magazine/2015/04/14/support-of-exposed-cable-for-pv-systems-requirements-and-recommendations/



Bundling 50-60 conductor together should have a much worse impact than working 
off the free-air table. I believe the only way to evaluate that bundle is to 
treat it as if it is in a raceway.



The lesser number of conductors (bundle of 3 or 4), the more it will begin to 
act like a free air cable.



Bill.





From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Brian Mehalic
Sent: Monday, August 31, 2015 2:56 PM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] Cable tray



Hello wrenches, question about running conductors in cable tray.  So we have 
our allowance in 690.31(C)(2) for using small PV Wire in cable tray for PV 
source and output circuits.  I'm trying to determine what adjustment factor to 
apply when there are a bunch of small conductors.



392.80(A)(2)(a) and (b) both address single conductor cable in covered cable 
tray, but only refer to conductors from 1/0 to 500 kcmil, and 600 kcmil and up. 
 I'm looking more at 40 or 50 12 AWG conductors (20 to 30 source circuits).  
The adjustment factors in 392.80(A)(2) are pretty hefty - only 60 to 70% of the 
rated ampacity, but as stated in Table 301.15(B)(17) (conductors in free air, 
so that helps).



Any guidance would be much appreciated, and thanks for your time,




Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59



PV Curriculum Developer and Instructor

Solar Energy International
http://www.solarenergy.org



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to