William,


I’m shocked and offended (a tiny bit) that you would prejudice yourself to not 
agree with me ;-).



First of all I have been heavily involved in the revising of the language in 
690.31(A) to make it clear that we cannot walk up and touch cables operating at 
600V. The term guarded is a defined term:



Guarded. Covered, shielded, fenced, enclosed, or otherwise

protected by means of suitable covers, casings, barriers,

rails, screens, mats, or platforms to remove the likelihood

of approach or contact by persons or objects to a point

of danger.



A fence actually does not prevent ready access (unless it does not have a 
gate), but the term guarded fixes that problem. The guarding means has to be 
approved by the AHJ, but many methods have been employed including mounting 
lattice work around the backside of fixed ground-mounted systems.



Fences are best used for larger systems (over 50-100kW) whereas other 
methods—albeit labor intensive—are generally preferred for smaller 
installations (under 100 kW)



No intelligent person would disagree with this proper interpretation of the 
NEC—including you.



Bill.





From: RE-wrenches [mailto:[email protected]] On Behalf 
Of William Miller
Sent: Friday, September 04, 2015 12:09 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Guarding against live parts 690.7 (D)



Ray:



1.    Why no fence?  Aesthetics.  Also costs may be a wash by the time you 
mobilize a fencing contractor.

2.    I’d apply the same requirements to a fence as one would to an uncovered 
swimming pool.  There are the same consequences if a child ends up in the wrong 
place.

3.    Why bother?

We figure the expense will decrease as we figure better design and 
implementation.  Hasn’t yet.

We care about safety.  I figure we, as an industry, will kill a child by 
electrocution someday—it is a matter of probability.  I hope it won’t be on one 
of our jobs.

We hope, in some small way, we influence the industry to improve.

4.    The industry has not developed solutions because there is no demand. 
There is no demand because AHJs don’t enforce the code.



Thanks for the compliment.  We have several new designs not yet featured on the 
web site. Check back next time this comes up.



William



PS:  I am curious what Bill Brooks take on this is, but I don’t think I will 
agree with his interpretation.



W






Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600



From: RE-wrenches [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of Ray Walters
Sent: Friday, September 04, 2015 11:37 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Guarding against live parts 690.7 (D)



WilIiam;

 checked out your guards on your website, that looks really clean, but also 
like a lot of work and expense.  I'm still so surprised manufacturers are not 
offering an option like that to their frame systems.
My question: how come you didn't just fence the array?  Shading issues on the 
south?
If fencing, what height of fence is considered adequate?  4 ft?  6 ft?



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 9/4/2015 9:44 AM, William Miller wrote:

Gary:



I think the issue of PV wiring behind module that are readily accessible is 
addressed in (2014) 690.31:



Where PV source and output circuits operating at maximum

system voltages greater than 30 volts are installed in

readily accessible locations, circuit conductors shall be

guarded or installed in a raceway.



I am not sure what application the original poster had in mind, but this is the 
question I think you are asking.  The interpretation to 690.31 seems clear to 
me:  No one should be able to touch the conductors without resorting to a 
ladder, opening a locked gate or removing a protective panel.  Readily 
accessible is defined thusly:



Capable of being

reached quickly for operation, renewal, or inspections

without requiring those to whom ready access is requisite

to actions such as to use tools, to climb over or remove

obstacles, or to resort to portable ladders, and so forth.



Implementing this is harder than it might seem.  Lacking a fence, the installer 
must either use the flimsy solar-scrim product or fabricate his or her own 
shielding.  We have put a fair amount of effort towards this.  See link 
<http://www.millersolar.com/MillerSolar/practices/PV_wiring/Wire_shielding/_Wire%20Shielding_history.html>
 .





William










Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600



From: RE-wrenches [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of gary easton
Sent: Friday, September 04, 2015 2:22 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Guarding against live parts 690.7 (D)



Bill

Are you  saying there is no requirement to shield wires on a ground array?

On Friday, September 4, 2015, <[email protected] 
<mailto:[email protected]> > wrote:

Craig,



This one is easy to misinterpret. You missed the words “live parts”. This has 
been removed from the 2017 NEC because it is actually referring to load 
circuits being fed directly by a PV system on the dc side. All references to 
loads and batteries are being removed from 690.



This is a complete non-issue.



Bill.



From: RE-wrenches [mailto:[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> ] 
On Behalf Of Craig Gerald Buttke
Sent: Thursday, September 03, 2015 11:44 AM
To: [email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: [RE-wrenches] Guarding against live parts 690.7 (D)





How is everyone handling 690.7 (D)

Circuits over 150 Volts to Ground. In one- and two- family dwellings, live 
parts in photovoltaic source circuits and photovoltaic output circuits over 150 
volts to ground shall not be accessible to other than qualified persons while 
energized.



If you have a commercial (non one or two-family dwelling) are you screening 
your ground mount arrays to keep people from touching live conductors PV wires)?

Thanks for your thoughts

--
Yours in Solardarity,

Craig Gerald Buttke

M:(715) 630-1227
O:(715) 630-6451
F:(715) 952-4501

North Wind Renewable Energy, LLC
1626C W Pearl Street
Stevens Point, WI 54481

www.northwindre.com <http://www.northwindre.com>

NABCEP Certified PV Installation Professional™
NABCEP Certified PV Technical Sales Professional™
State of WI: Master Electrician



  _____


 <https://www.avast.com/antivirus>

This email has been checked for viruses by Avast antivirus software.
www.avast.com <https://www.avast.com/antivirus>





--
Sent from Gmail Mobile





_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>






---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to