Drake,

Quote: “...and goes right back to that voltage in the morning.”

How quickly does the battery voltage rise to 29.1 in the morning? If the 
batteries are sulfated heavily, you may see a very fast rise in voltage but you 
will also see a loss of capacity. Batteries in the early stage of sulfation may 
have a difficult time reaching the constant voltage setpoint and remain in bulk 
charge continuously.

What is the size of the PV array and battery bank? If the array is too small 
for the bank, this is the time of year (less sun hours per day) that we start 
to receive complaints about the battery not getting charged.  

Larry Crutcher
Starlight Solar Power Systems

On Sep 9, 2015, at 5:06 PM, Drake <[email protected]> wrote:

Hello Wrenches,

I have a Morningstar PWM 45 that doesn't drop out of absorb. It is set with dip 
switches to absorb at 29.2 V and stays constant around 29.1. It has stayed at 
29.1 for several hours straight, and goes right back to that voltage in the 
morning. Tech support says the controller is working correctly. Have any of you 
seen this, or conversely have you seen the Morningstar drop into float after a 
reasonable amount of time?

Thanks,

Drake 


 <>Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV 
740-448-7328
http://athens-electric.com/ <http://athens-electric.com/> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to