If the inverter were in search, I would think that there would be no AC power produced by
the micro inverters at all because of anti-islanding.

boB


On 9/21/2015 4:40 PM, Jay wrote:
Nope wasn't in search when I had flicker.
If the loads were greater than the enphase production then no flicker.

If it was "charging" then there was flicker.

My vfx 3524 is 8+ years old, but I don't think that would be a factor.

Jay.



Sent from my iPhone

On Sep 21, 2015, at 12:46 PM, jerrysgarage01 <[email protected] <mailto:[email protected]>> wrote:

Wrenches
Check and confirm that the OB is not set in search, yhis will cause issues like this.
Jerry



Sent from my Verizon Wireless 4G LTE smartphone


-------- Original message --------
From: jay <[email protected] <mailto:[email protected]>>
Date: 09/21/2015 6:58 AM (GMT-10:00)
To: RE-wrenches <[email protected] <mailto:[email protected]>> Subject: [RE-wrenches] AC-coupling Enphase/XW Causes Flickering of Lights

Hi Matt,

I can’t tell you the reason but I had the same problem on my Outback VFX.
I didn’t put it on a O scope, but sure looked like a 60 cycle flicker to me.

On my system of 2 enphase, when the loads exceeded the output of the enphase the flicker when away.
But only 2 isn’t very real world.

In the end it was just a test for me, and it didn’t work.

jay

peltz power
On Sep 21, 2015, at 6:18 AM, Matt Sherald <[email protected] <mailto:[email protected]>> wrote:

I wired an Enphase string into my critical loads panel at my shop. I was curious to see how it would work as I have customers with Enphase systems that occasionally contact me about adding a battery backup system.

Why do the fluorescent lights and LEDs flicker once the grid power is dropped. The flicker seems to start as soon as there is enough sun to power up a few of the micros (they don't even have to be making much power).

The shop is grid-tied with a XW 4024 for battery backup. Battery capacity is 370Ah.

I'd love an explanation as to why this happens and if there is a way to mitigate the flicker I would also love to hear it.

Many thanks!

--
Matt Sherald
PIMBY Energy, LLC
NABCEP Certified Solar PV Installer®
304-704-5943

www.getpimby.blogspot.com <http://www.getpimby.blogspot.com/>
www.getpimby.com <http://www.getpimby.com/>


_



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to