While we are discussing this, I have a suggestion. We are using the Generac
Smart Management Module as a load management unit for generators. It
automatically senses that the power is coming from the generator. It has a
lock out mode, so it can be used to disconnect the inverter(s) when the
generator is running without needing any wiring. I anticipate this to save
a lot of cost and allow a more robust system when combining generators and
inverters.

On Tue, Oct 20, 2015 at 12:25 PM, Chris Mason <[email protected]>
wrote:

> He's wrong. Any inverter system will try to raise the voltage of the
> system, that's how grid tied inverters feed power to the load. With the
> utility grid, there is no issue as the inverter cannot move the voltage any
> significant amount (unless there is a high resistance point). With a
> generator which is also trying to feed the same load, as the inverter's
> output power comes close to the load, the voltage will rise and the
> generator's AVR will get confused. It will reduce the excitation to the
> alternator and will likely start to motor if the inverter's power output
> exceed the load. The generator can shut down if the the system voltage
> exceeds the high voltage setpoint, and other bad things can happen such as
> damage to the AVR and stator windings. There's no real way to know what
> will happen. In many cases where the load exceeds the inverter output,
> nothing bad happens, but it's a crap shoot.
>
> On Tue, Oct 20, 2015 at 12:01 PM, Howie Michaelson <[email protected]
> > wrote:
>
>> Does anyone think that there is no issue with having enphase potentially
>> backfeeding a backup generator? We almost always will tie in upstream of a
>> generator transfer switch, but a competitor is telling clients with an
>> enphase system there is no concern. Am I missing something?
>>
>> Thanks,
>> Howie
>> Howie Michaelson
>> NABCEP Certified Solar PV Installerâ„¢
>>
>> Catamount Solar
>> Renewable Energy Systems Sales and Service
>> VT Solar Electric Incentive Partner
>> http://www.CatamountSolar.com
>> 802-272-0004
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installerâ„¢
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com <http://www.cometenergysystems.com>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
>



-- 
Chris Mason
NABCEP Certified Solar PV Installerâ„¢
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to