My hunch is that you have four strings of 11 modules and 1 of the four strings 
is wired backwards such that the DC+ goes to the negative input of the 
inverter, and the DC- of the string to the fused DC+ of the inverter.  This 
would look fine under open circuit conditions, but not perform properly when 
connected.  But it is impossible to tell from the information given.  Jay’s 
advice to test with each string individually would be the way to go.

 

Mike Kocsmiersky

Principal

Phone: 413 883-3144 

Spirit Solar

www.SpiritSolar.net

 

 

From: jay [mailto:[email protected]] 
Sent: Thursday, November 19, 2015 11:31 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Friend with system needs help

 

HI Steve,

 

So they are all low?

 

Then I suggest an IV curve tracer.

 

 

jay

 

 

On Nov 19, 2015, at 7:18 AM, Steve Jefferson <[email protected]> 
wrote:

 

The outputs are pretty close. That’s what is throwing me off.

In most trouble shooting adventures, the problem is fairly obvious.

This one, not so much.

 

SMA America, LLC

Steve Jefferson

Service Line Supervisor

3925 Atherton Ave

Rocklin, CA 95765 - 3714

U.S.A.

Tel:  +1 916 625 3185 (direct)

Fax: +1 916 625 0871

Mobile: +1 916 622 4253

Email:  <mailto:[email protected]> [email protected]

 <http://www.sma-america.com/> www.SMA-America.com

 

 <http://www.youtube.com/watch?v=yQWzPuyqhzo&feature=youtu.be> <image001.png>

 

This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

 

 

From: RE-wrenches [ <mailto:[email protected]> 
mailto:[email protected]] On Behalf Of Jay
Sent: Wednesday, November 18, 2015 1:42 PM
To: RE-wrenches < <mailto:[email protected]> 
[email protected]>
Subject: Re: [RE-wrenches] Friend with system needs help

 

Hi steve. 

 

Is the output from each string of 11 the same?

Have you tried ruining 1 string at a time?  

 

Jay



Sent from my iPhone


On Nov 18, 2015, at 11:14 AM, Steve Jefferson < 
<mailto:[email protected]> [email protected]> wrote:

Afternoon wrenches,

 

I have a friend who I helped install second hand modules onto a pergola 
structure at their home.

 

The system is as follows:

 

44 – Siemens SP-150

1 – SMA SB6000US-12 (XFMR unit)

 

Since install, they have not produced half of what they should be.  I have 
tested the diodes and they seem to be good, there were a couple that tested 
questionable, so they were replaced.

VOC is good, but it seems that under load the system goes to garbage.

 

I am at a loss of what/how to test anything else that may determine cause.

 

Would a PV Analyzer help? Would there happen to be anyone in the Sacramento 
area with one who could come to the site? Obviously the customer will pay for 
their time.

 

Thanks in advanced.

 

SMA America, LLC

Steve Jefferson

Service Line Supervisor

3925 Atherton Ave

Rocklin, CA 95765 - 3714

U.S.A.

Tel:  +1 916 625 3185 (direct)

Fax: +1 916 625 0871

Mobile: +1 916 622 4253

Email:  <mailto:[email protected]> [email protected]

 <http://www.sma-america.com/> www.SMA-America.com

 

 <http://www.youtube.com/watch?v=yQWzPuyqhzo&feature=youtu.be> <image001.png>

 

This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address:  <mailto:[email protected]> 
[email protected]

Change listserver email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
<http://www.mail-archive.com/[email protected]/maillist.html> 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
 <http://www.members.re-wrenches.org/> www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address:  <mailto:[email protected]> 
[email protected]

Change listserver email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
<http://www.mail-archive.com/[email protected]/maillist.html> 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
 <http://www.members.re-wrenches.org/> www.members.re-wrenches.org



 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to