I use the egauge a lot. Although it is not circuit specific, you can tell
from the profiles what is taking power. You have 12 inputs so you can use
it on 12 circuits instead of just the overall service.
If you buy 50A CTs they are pretty cheap.
The Homeplug adapter makes getting the data to the internet very easy.
I don't think you will find anything cheaper and easier.
I have a spare unit I keep as a site assessment tool. Even though we have a
Fluke 435 Energy Analyzer, the egauge is better for longer period
assessments.
Also, you can cascade them so if you have two panels in different locations
you can use one as an input to the other.

On Fri, Dec 11, 2015 at 9:17 PM, jay <[email protected]> wrote:

> HI All.
>
> I’ve been getting a bunch of requests for better monitoring of AC
> circuits, and I want to be able to understand some peoples loads better as
> well.
> This is for a full house 120v  and  240v
> And
> individual circuits.
> I don’t need revenue grade.
> But looking for something that is easy to use, maybe blue tooth app, or
> digital display with memory ( day/week/month would be good)
> Could be internet connected but not a priority.
>
> I’ve seen some for $40-80.
>
> There are so many out there I figure someone/s have got some fav’s.
>
> thanks
>
> jay
>
> peltz power
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to