Thanks Guys, for the feedback. 

I reduced the system to one string when I was on site, and it is maintaining, 
though the remaining "good" batteries had a lot of variance in the SG between 
cells.

I don't think the cells in these particular batteries are removable (at least 
not by me), as the interconnections are welded and it does not look like it 
would be easy to pull them out of the case anyway. As Jay pointed out, even if 
that were possible, replacing the cells with new ones seems like throwing away 
money.

The charge parameters were set kind of low ~58V Bulk and 61V EQ.

 I know the homeowner has not been using SG to equalize, as he doesn't even 
have a way to check the SG period.

Tommy Penson was kind enough to contact me off-list, and his recommendation was 
to increase the charge parameters and spend some time trying to bring the bad 
cells back up with careful charging and longer EQ cycles.  Seems like that is 
worth doing even if it's not successful, considering the expensive alternative.

-Luke





On Dec 16, 2015, at 1:44 PM, Dana <[email protected]> wrote:

> Try Tommy Penson at North West Energy Storage at 800.718.8816
> 
> ----------------------------------------------------------------------------
> Dana Orzel 
> Great Solar Works, Inc -  NABCEP # 051112-136
> E - [email protected]  - Web - solarwork.com 
> O - 970.626.5253  C - 208.721.7003
> "Responsible Technologies for Responsible People since 1988"  
>  Please consider the environment before printing this email.
> 
> 
> 
> -----Original Message-----
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of Dave
> Sent: Wednesday, December 16, 2015 10:23 AM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] HuP Conundrum
> 
> Luke,
> 
> Contac HUP for specific advice. You've probably already done that?
> 
> What comes to mind:
> Since you have two series strings, run the house on one string of all good 
> cells.
> 
> Pull out the weak cells and charge them as per HUP's advice.
> 
> I'm guessing that this problem has happened because the homeowner did not 
> properly charge the batteries.
> Homeowner most likely did not use a hydrometer upon EQ'ng the cells.
> Homeowner thought the cells were fully charged and equal but obviously they 
> were not.
> Record keeping, log books etc.. for people caring for expensive batteries are 
> well worth the effort.
> 
> David Palumbo
> Independent Power LLC
> 462 Solar Way Drive
> Hyde Park, VT 05655
> 802-371-8678 cell
> 802-888-4917 home
> 
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to