No "settings recommend by Trojn"were shown. 
> On Jan 18, 2016, at 6:43 PM, William Miller <will...@millersolar.com> wrote:
> 
> Colleagues:
>  
> I have an off-grid customer for whom I replaced a set of 8 Trojan L-16s as 
> well as upgrading her inverter and charge controller.  Right after the job, 
> we found several batteries with low specific gravity.  We spoke with the 
> local distributor and received two replacement batteries.
>  
> The system continues to perform poorly.  The customer EQs every 30 days to 60 
> plus volts for 3 hours.  They try to get a full bulk and absorption charge in 
> every day but this time of year may not. The specific gravity readings 
> continue to diverge and generally go lower.
>  
> We contacted the distributor who told us they have had problems with Trojan 
> batteries since the company was sold about two years ago.  We were told they 
> had a brand X battery that tested better than the Trojans.  We agreed to try 
> the Brand X but then were told that we had not charged the Trojans 
> adequately.  Below are the settings recommended directly by Trojan
>  
> These settings are significantly higher than any I have used before.  Also, I 
> don’t recall it being possible to set different bulk and absorption voltages 
> with any of the equipment I use.  I use Trace, Outback, Schneider default 
> settings of 57.6 bulk, 54.4 float and reprogram to 60.5 for equalization.
>  
> I am curious about what charge settings you find successful for flooded 
> lead-acid batteries and what any of you might think about the recommended 
> settings as seen below. Do you feel it is practical to achieve these settings 
> in an off-grid scenario?  Would these high settings cause excessive water 
> consumption?
>  
> Thanks in advance.
>  
> William Miller
>  
> <image001.jpg>
> Lic 773985
> millersolar.com
> 805-438-5600
>  
>  
>  
> I looked at the spreadsheet and the SG. readings across each battery are 
> uniform which tells be that it is highly unlikely that anything is wrong with 
> the batteries except for being under-charged. Take a look at our User’s Guide 
> on the Trojan website on page 19  ( Recommended Charge Profile) or FLA 
> batteries.
> The Bulk stage should be @ 59.3V, Absorb @ 58.8V, Float @ 54V and 
> Equalization @ 64.8V. When the User notices drops in the SG such as in this 
> document, an EQ charge should be performed in order to get the batteries back 
> up to full charge (full charge SG being in the range of 1.270 to 1.280. When 
> performing the EQ, the user should take SG reading for a “pilot” battery 
> every 30 minutes until the voltages reach that range. Termination should 
> happen when SG reaches full charge range or if battery temperature reaches 
> 112 degrees F, which-ever comes first. SG readings can be taken during EQ, 
> but you have to make sure that you bump the tiny gas bubbles off the 
> Hydrometer float to prevent erroneous readings.
> Seeing the SG readings decreasing after each month is an indication that 
> maybe the Absorb Time needs to be increased, maybe from 3 hours up to 4 or 5 
> hours.
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to