Howie,

 

To clarify what the 2017 NEC states, it allows for either end of the bus. There 
is some value to having loads in between the PV breaker and the main breaker. 
Also, by putting the PV breaker as far away from the main as possible, the heat 
of both breakers are likely to affect each other. 

 

The 2005 and earlier NEC did not stipulate anything about location on the bus.

 

Bill.

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Howie Michaelson
Sent: Thursday, March 03, 2016 12:11 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for 
center-fed panelboards

 

Bill,

Did I understand your earlier post to infer that there never was an intent to 
apply the "opposite end of the buss" rule to the 120% backfeed allowance in 
residential applications?  And that you have been working to rewrite a solar 
backfeed breaker in a residential setting to land anywhere on the buss?

Howie


Howie Michaelson
NABCEP Certified Solar PV Installer™
Sun Catcher, LLC
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004

 

On Thu, Mar 3, 2016 at 12:07 PM, <[email protected] 
<mailto:[email protected]> > wrote:

Phil,

 

I think you already understand how to apply the “120% rule.” All this is saying 
is that the breaker can go at either end of a center-fed panel for dwellings. 
Do you understand now?

 

To summarize—a 200A center-fed panel would allow a 40-amp PV breaker to be 
installed at either end to meet the 120% rule.

 

Bill.

 

From: RE-wrenches [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of Philip Lawes 
Insoltech
Sent: Thursday, March 03, 2016 8:26 AM
To: 'RE-wrenches' <[email protected] 
<mailto:[email protected]> >
Subject: Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for 
center-fed panelboards

 

Bill,

Could you please provide an example of this showing calculations?

Thanks so much,

Phil

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of [email protected] <mailto:[email protected]> 
Sent: Wednesday, March 2, 2016 11:24 AM
To: 'RE-wrenches' <[email protected] 
<mailto:[email protected]> >
Subject: Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for 
center-fed panelboards

 

All,

 

Here is the new language that has been approved for the 2017 NEC (more 
authoritative than JW).

 

705.12(B)(3)(d)

 

(d) A connection at either end, but not both ends, of a center-fed panelboard 
in dwellings shall be permitted where the sum of 125 percent of the power 
source(s) output circuit current and the rating of the overcurrent device 
protecting the busbar does not exceed 120 percent of the current rating of the 
busbar.

 

This clarifies that it was never the intent of the NEC to limit the 120% rule 
to the opposite end of the busbar for dwellings (it was allowed from 2005 back 
to 1987). I was able to convince the panel that centerfed panels did not need 
the opposite end stipulation. Several large jurisdictions in California or 
considering making an official policy accepting the language of the 2017 NEC on 
this item. Please share this with your own jurisdiction.

 

Bill.

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Glenn Burt
Sent: Wednesday, March 02, 2016 10:54 AM
To: RE-wrenches <[email protected] 
<mailto:[email protected]> >
Subject: Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for 
center-fed panelboards

 

I believe that John Wiles has stated this in a couple of places in print, 
therefore you may have a tough time justifying a way around the rule to an AHJ.

Supply side connections are very popular in this situation.

  _____  

From: August Goers <mailto:[email protected]> 
Sent: ‎3/‎2/‎2016 11:32
To: RE-wrenches <mailto:[email protected]> 
Subject: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for 
center-fed panelboards

All –

 

We are seeing more AHJs not allowing us to use the NEC 7015.12(D)(2)(3)(b) 120% 
rule on center-fed panelboards. For example, if we have a 100 A meter/main 
combo with a center fed 100 A breaker we cannot apply the 120% rule at all and 
need to do a panel swap. What are other wrenches doing in this case?

 

Best,

 

August

Luminalt


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 



 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to