Have installed a 5548 and 6048 XW with  IG Plus 10.0 with fair results.
On/Off when AC coupled during the test phase. I have not heard any complaints 
from the homeowner.

Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand!

On Apr 4, 2016, at 1:34 PM, Allan Sindelar 
<[email protected]<mailto:[email protected]>> wrote:

Wrenches,
Core question first: Will a ~2010 Fronius IG-4000 respond properly to the 
frequency shift regulation supplied by a new Schneider XW+5548 or XW+6848?

Situation: I haven't seen the Colorado site; I'm working as a consultant to 
produce an upgrade component list and will later serve as a resource during 
local installation of the upgrade equipment. Customer has hired me to turn a 
hodgepodge system into a GTBB system. The system has two key parts: an existing 
SW5548 with batteries, never properly installed (only AC1 in was ever connected 
to a main load center!) with 3.1 kW of tracker-mounted PV through an Outback 
FM60; and a roof-mounted 4kW array feeding the grid panel via the IG-4000. As 
currently installed, nothing will operate as wired during a grid outage, and a 
240V AC well pump isn't supported.

The simple plan is to replace the SW5548 with an XW+5548 or 6848 with Midnite 
E-Panel; replace batteries with Surrette FLAs; keep existing arrays unchanged; 
use existing FM60 for smaller tracked array; use existing Fronius IG-4000 but 
AC couple it to the output of the XW. The customer understands that sell 
amperage is limited by the inverter (to 20A @ 240V for the 5548, or 4,800W, or 
27A @ 240V for the 6848, or 6,480W) when the grid is up, but the full array can 
charge the battery bank when the grid is down.

Schneider tech support assures me that the XW+ is good in this application, but 
I need to get an OK from Fronius about frequency-shift compatibility. Fronius 
tech support tells me that it may or may not work: the 0.4 hz shift is within 
the the normal frequency tolerance for this model. While the tolerance window 
may be tightened up in the field, such tightening may cause nuisance tripping, 
especially with reactive loads like a well pump or A/C. The tech suggested that 
we first test the frequency-shift approach, and add a DC-coil contactor between 
the output of the Fronius and the XW+ if it doesn't.

Has anyone AC coupled these two units? Did it work? Any unexpected problems? 
Did you add a voltage-controlled contactor? What should I advise my client?
Thank you,
Allan
--
Allan Sindelar
<mailto:[email protected]>[email protected]<mailto:[email protected]>
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell


_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to