You should find your answers in 310.15

Patrick A. Shortell
Licensed Master Electrician
Certified Solar Installer
71 Oregon Street
Long Beach N.Y. 11561
Www.thesolarstorehouse.com


> On Apr 21, 2016, at 11:56 AM, Peter Parrish <[email protected]> 
> wrote:
> 
> I am working with a customer who is doing a complete remodel and addition to 
> his house: stripped to the open studs and floor joists, and rafters. Not a 
> wire in the house. We have designed a 14.4 kWp PV system with 16 kW of 
> storage for backup and load shifting. The main panel, inverters, critical 
> load subpanel and batteries are all going to be in the garage which is about 
> 45 feet from the house. The customer and I have identified the critical loads.
>  
> The GC is running conduit from the main house to the garage. I have been 
> given seven (7) 1-1/2” PVC conduits, and I am currently doing conduit fill, 
> ampacity and voltage drop calculations for the branch circuits that represent 
> the critical loads.
>  
> So I have two questions:
>  
> (1)    Should I stick to a <1% voltage drop on all circuits?
> (2)    Do 120 V neutrals count as current carrying conductors? I think they 
> do, but the electrician stated quite emphatically that  they didn’t. I 
> thought that the derating calcs for CCCs were based solely on ohmic losses 
> and phasing was not taken into account.
>  
> Does the NEC provide guidance on this latter situation?
>  
> -          Peter Parrish
>  
> Peter T. Parrish, Ph.D.
> President, SolarGnosis
> 1107 Fair Oaks Ave.
> Suite 351
> South Pasadena, CA 91030
> (323) 839-6108
> [email protected]
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to