ChrisA few questionsAre you drawing from both AC legs from the genny, at max of
2200 watts per leg then the genny should not have an issue but if you upsized
the batteries and as stated by Mike the fuel delivery system cant keep up
because the inverter charge load is higher, steady and for long duration. Can
you load test the genny at 240 and see if the issue happens with out the
inverter at all. When we size a propane tank we like to see at least 75 lbs
per 3 kw genny depending on air temp, bigger when colder, its all about
available BTU.Jerry
Sent from my Verizon Wireless 4G LTE smartphone
-------- Original message --------
From: Mike Kocsmiersky <[email protected]>
Date: 4/26/2016 12:41 AM (GMT-10:00)
To: 'RE-wrenches' <[email protected]>
Subject: Re: [RE-wrenches] Battery charging problems
Chris,
In theory the upgraded batteries should be able to accept a greater current
(or at least max charge current) for a greater length of time than the prior
battery bank. I once had a propane genset run rough when it was starved for
fuel, due to an undersized upright propane cylinder which could not
evaporate the liquid propane fast enough for the load of the genset. This
caused the regulator on the genset to have awful difficultly, and usually
would drop the load because it couldn't stabilize. This doesn't sound like
it would be your problem, if it was running properly before, but perhaps the
longer duration at higher current is creating difficulty for the LPG to
evaporate enough. May be compounded if the fuel tank was recently
overfilled and doesn't have as much surface area, or if it is way low and
can't maintain pressure. May want to check the tank size of propane for the
genset. (I'm assuming this is LPG).
Mike Kocsmiersky
Principal
Phone: 413 883-3144
Spirit Solar
www.SpiritSolar.net
-----Original Message-----
From: Chris Daum [mailto:[email protected]]
Sent: Thursday, April 21, 2016 3:41 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Battery charging problems
Dear people:
I have an off-grid customer who has, in his system, a Magnum MS4448 and 16
of the Rolls S550 batteries, a Kohler generator (and Trimetric meter and
other components). He upgraded his batteries this past March, and since
he's installed his new batteries, the generator is running 'rough'. He's at
a great distance from our shop so a local business helps him from time to
time. They believe that the "batteries are too powerful for the 8.5 kw
generator" and recommended running it at 50 percent charge control. After 3
hrs run, it seems to help but will mean more run time for his generator (and
hence, use more fuel). Have you ever heard of anything like this?
Everything ran fund before the battery upgrade.
Thanks for your input!
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-0830 fax
www.oasismontana.com
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org