Does the generator need to feed an inverter /charger input? In other words,
does it need to provide AC/60hz?

If it can be a DC genset (which is usually easier on the system) check out
Polar Power.  http://www.polarpower.com/


Roy Rakobitsch
NABCEP Certified Small Wind Installer®
Certified Advanced Tower Climbing, Safety & Rescue
Wind/PV Design Engineer
Windsine LLC
631-514-4166
www.windsine.org




On Thu, Apr 28, 2016 at 6:00 PM, jerrysgarage01 <[email protected]>
wrote:

> Have you looked at Cummins,  we have have great luck and no programming
> issues but battery charging needs to be added foroff grid
> Jerry
>
>
> Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
>
>
> -------- Original message --------
> From: Ray Walters
> Date:04/28/2016 7:28 AM (GMT-10:00)
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Off-grid generator update?
>
> FYI,  generally we haven't had cold start issues with propane units, as
> long as the pipe is sized properly ( as mentioned in another recent post)
> and the starter battery is kept fully charged.
> This is based on about 20 years experience in the Rockies with temps below
> 0, but not 40 below.  We don't use block heaters, carb heaters, etc.
> We currently have been using Generac Ecogen, but not that happy with them.
> Cheap air cooled motor, way too many computer gizmos, no on board charging
> (must have AC power or PV to charge the starting battery)  We even had to
> call customer service to get an authorization code to set up remote start.
> This is off grid with no internet or cell service; ridiculous.  I hope
> Generac reps are lurking here, because these are really not much better
> than the crop of stand by generators.
>  IMO  no off grid generator should have a phantom load, or require cell
> service to commission.  What happened to the old water cooled Kohlers?
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer303 505-8760
>
> On 4/28/2016 11:17 AM, Jeremy Rodriguez wrote:
>
> Check out Gillette generators. Made in Indiana
> 12.5 kW w Subaru
>
> Jeremy Rodriguez
> Solar Installation And Design Expert
> All Solar, Inc.
> 1463 M St
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand!
>
> On Apr 28, 2016, at 10:20 AM, Lena Wilensky < <[email protected]>
> [email protected]> wrote:
>
> I did some searches on the list for what folks are doing for off-grid
> propane generators these days, but all the threads I found were from 5-6
> yrs ago, so I was hoping to get some more current info.
>
> We're looking for about a 10kw+ propane unit (big derate at altitude), and
> we run into 2 main problem areas:
>
> First is the warranty - either there are no units warranteed for off-grid
> use, or there are only a couple of models and the warranty is short (1
> year).
>
> Second, and perhaps larger, is all the loads that now come with the
> "off-grid" units.  The computer takes some, but mostly the "cold weather
> kit" aka carb heater must be installed in our climate (to actually start,
> but also for warrantee), and it's set up to be on a thermostat (read: "on
> all the time from Nov-April" here in the mountains).  According to the
> Kohler tech support it takes a steady 50W. We have set up older units to do
> battery charge only during the day, and have the carb heater on a manual
> switch, but it sounds like we can't really get at these circuits anymore
> since they're all pre-configured and pre-wired in the guts of the genset
> computer.
>
> The Kohler and Onan support folks said both these issues are due to EPA
> considering off-grid use as prime power as opposed to standby, so they are
> held to tougher emissions standards.
>
> Whatever the reasons, we're wondering what people are actually doing these
> days - still the standby units they kind-of warrantee for off-grid? 12RES
> from Kohler and the 13kw unit from Onan?  Generac?  Have folks been going
> back to the smaller gas units from Honda and running them more?  And how
> are cold climate folks dealing with the heating issue?
>
> Any suggestions appreciated!
>
> Lena Wilensky
>
> www.nunatakenergy.com
> 970-642-5554
> NABCEP Certified PV Installer:
> Cert. #R02907-17
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to