Hi Dave, I have quite a few of the 6kW EcoGens out in the field and I haven't seen this issue come up (thankfully).
I suspect the issue lies in the the scavenging probe or plumbing for the pump system. The probe is supposed to set the fill level for the crankcase, but since it is basically just a tube projecting down to the oil level, I'd first take a hard look at the associated tubing and check valves. There could be a failed diaphragm or a stuck check valve that's stopping the scavenging action of the pump system. It could also be a chunk of goo or something in the scavenger probe. You have oil going into the crankcase from the reservoir, but no oil being removed. As I understand it, the system is supposed to enable a longer service time between oil changes by effectively using the entire volume of oil in the reservoir and the crankcase. The oil is slowly pumped into the crankcase sump from the reservoir, and simultaneously pumped back out into the reservoir, while maintaining the correct fill level in the sump --as long as everything works properly. Have you checked out the plumbing diagram in the back of the installation manual just to confirm that the hoses are routed correctly? If the unit has operated ok for 1,000 hrs, that can't really be the issue unless a hose has cracked or has a vacuum leak at a fitting. I personally don't see an issue with draining the reservoir and sump and filling the crankcase back to the correct level so that you can run it on a temporary basis, but you will definitely want to get it fixed for the long term. -Luke Luke Christy NABCEP Certified PV Installation Professional™: Certification #031409-25 NABCEP Certified Solar Heating Installer™: Certification #ST032611-03 Solar Gain Services, LLC PO Box 531 Monte Vista, CO. 81144 [email protected] 719.588.3044 www.sgsrenewables.com On Apr 29, 2016, at 9:59 AM, "Dave" <[email protected]> wrote: > Wrenches, > > I service an off grid home that has an EcoGen 6kW Model 58181 LP gen with a > Serial Number of 8301854. It has 1,175 hrs on it during 2-1/2 years of > service. > > · It appears that the crankcase is filling with excessive amounts of > oil. > · There was a Generac Service Bulletin in July of 2013 which predates > this generators Serial Number. This bulletin alerted the possibility of > excessive oil in the crankcase due to "incorrect routing of the pulse pump > hoses". > · From the pictures on the service bulletin (and with the SN being > higher) it looks like the generator in question has properly routed hoses. > See photo attached if you are familiar with this problem. > · There is an extra oil reservoir on these units. The engine takes > 1.7 quarts and the reservoir takes 4.2 Quarts. > · I last changed the oil (and properly filled both engine and > reservoir) at 1,124 hours > · Now at 1,175 hrs the generator runs very roughly and blows lots of > oily smelling blue/grey smoke. Most of the oil is gone from the reservoir so > it's pretty obvious that the oil has flooded into the crankcase. > · If the Pulse Pump hoses are routed correctly and I'd say they are > since the SN is later than the recognized problem AND the fact this generator > ran great for over 1,100 hours then maybe is the pulse pump itself is bad? > · I wanted to run this by this list before talking to Generac because > I know there are a number of wrenches whom have experience with the EcoGen. > · Can I simply just drain the oil and only refill the 1.7 Qts in the > engine and run the unit? > > Thanks for your time, > > David Palumbo > Independent Power LLC > 462 Solar Way Drive > Hyde Park, VT 05655 > 802-371-8678 cell > 802-888-4917 home > > <Generac ECO Gen 5818 1.jpg>_______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/[email protected]/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org _______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org

