A FLA that has been completely FULLY charged & disconnected will not require any servicing.
There IS a device called a main battery breaker that should be shut OFF as should both the Charge controller breakers. IF the system has a trimetric while it is a pain to reset I recommend that these too are on a breaker that should be shut off.
Any FLA battery that has been EQed and has had its Spg checked and recorder above 1.26+ will be fine for an extender period of time.
Charge controllers WILL become parasitic loads during the winter if not disconnected. They will see a bit of voltage when the modules are covered w/ snow but there is NOT enough light to create current and thus becoming a load. Expecting the cc to function without some glitch for the winter is a disaster waiting to happen. 
Reoccurring revenue stream is offering to visit site twice a year and perform  the afore mentioned tasks. You can also train customer the first few times.

On May 1, 2016, at 8:23 PM, wmdorsett <[email protected]> wrote:


Mark, this is fairly typical of the group thought around flooded lead acid batteries. ..they very often conclude with speculation about a new battery chemistry. 

Bill


Sent from my Verizon Wireless 4G LTE smartphone
-------- Original message --------
From: Dana <[email protected]>
Date: 4/30/2016 12:54 PM (GMT-08:00)
To: 'RE-wrenches' <[email protected]>
Subject: Re: [RE-wrenches] Winter Battery Maintenance

I have yet to see any FLA battery that can go 4-5 months without service. Typically a FLA needs an increased voltage to attain the same full charge rating at low temps, but you still require watering. I have clients with shut down houses and no load situations, we back off the Absorb set point voltage, & time at full & they still require watering.

This thread started with “? I don't think the friend will be savvy enough to disconnect/connect them every year and I don't feel like having to go out there every season for them.”

 

Based on this statement would you still recommend FAL batteries? I have clients with AGMS that are partial year residents & their AGMS are at 8-10 years and still doing the job. That said some clients even full time occupants cannot water & test the SG on a FLA to save their life (or sustain the batteries life).

 

----------------------------------------------------------------------------

Dana Orzel

Great Solar Works, Inc -  NABCEP # 051112-136

E - [email protected]  - Web - solarwork.com

O - 970.626.5253  C - 208.721.7003

"Responsible Technologies for Responsible People since 1988" 

P Please consider the environment before printing this email.

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf Of Starlight Solar Power Systems
Sent: Saturday, April 30, 2016 1:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Winter Battery Maintenance

 

I agree with Todd and Bob, leave the PV solar on, EQ off. 

 

I also instruct my customers to reduce the absorb timer to 0.1 hours. Since the battery is staying full, there is no need to spend time above cell gassing point which will increase water loss.


Larry

 

 

On Apr 30, 2016, at 10:28 AM, RE Ellison <[email protected]> wrote:

 

Everything mentioned so far works well however, if you're using a charge controller with an auto equalize function.

 

Turn it off!

 

I had a friend who has left his system over the winter for years with no issues and he shut his inverters off one year got back to the batteries being boiled dry

 

After a lot of looking I figured out that it had gone into auto equalize and since the available sunshine per day was so low that it just kept trying all winter long to equalize the batteries

 

There was a battery replacement in his future relatively quickly!

 

It was an expensive lesson and I have since gone to all of the systems similar to that that I have installed over the years and shut off the auto equalize

 

It's not an issue if somebody's around but they were gone for like five months and it was not a good outcome

 

This particular system had three charge controllers,

A combination of MX 60 and FM 60s I believe

 

Just my thoughts,

Bob ellison

 

 

 

 


On Apr 30, 2016, at 12:43 PM, [email protected] wrote:

i built a system for a friend's seasonal (summer) off-grid residence in alaska.

 

my instructions were simple:

leave the pv input & cc output breakers "on" and the load breakers (inverter, dc sunfrost etc) "off".

 

there was never a problem with winter freezing (even at -40f) until one year when he accidently left the inverter's breaker on. even with no load, the inverter's idle current drained the batteries and they froze. he only made that mistake once.

 

todd

 

 

 

 

 

On Saturday, April 30, 2016 8:13am, "Solar" <[email protected]> said:

> I do systems like this every year. (-45F winter temps). Use quick connects and
> train the customer on the batteries and their maintenance. Find bats with freeze
> points that match your area. I typically mount the modules at 90degree so snow
> never covers the array/module.
>
> I always recommend removal. I've thought about temp controlled incandescent lamp
> with a timer in a battery box for really cold nights.... Haven't got around to
> working through that design.
>
> I'm interested in the real seasoned off-grid installers thoughts about this.
>
> Jesse Dahl
>
> NABCEP PV Installation Professional
> IBEW Local 292 - Electrician
> Electrical/Solar PV Instructor - HCC
>
> Sent from my iPhone
>
> > On Apr 30, 2016, at 9:07 AM, AE Solar <[email protected]>
> wrote:
> >
> > Hey Wrenchers,
> >
> > A friend wants a very small battery set up at hunting cabin (like under 1kW).
> It will only be used in the warmer months. I'm wondering what you all recommend
> for the batteries over the winter. I assume the ideal situation would be that they
> would be disconnected and brought somewhere warm for the winter (the cabin will be
> subject to below freezing temps)??
> >
> > So long as they go into the colder months with a full charge is it alright to
> leave them hooked up? I don't think the friend will be savvy enough to
> disconnect/connect them every year and I don't feel like having to go out there
> every season for them.
> >
> > Thanks for any thoughts.
> > Adam
> >
> > Adam Katzman
> > Autonomous Energies
> >

 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to