In Vermont, our largest utility approves of and actually sells the Connectder 
meter collar at a discount – which of course requires the meter to be pulled. 
AND they allow the non-electrician installer to pull and reinstall it in 
single-family residential applications.

 

Kirk Herander

Owner|Principal, VT Solar, LLC 

Celebrating our 25th Anniversary 1991-2016

www.vermontsolarnow.com

dba Vermont Solar Engineering

NABCEPTM  2003 Inaugural Certificant

VT RE Incentive Program Partner

802.863.1202

 

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of August Goers
Sent: Wednesday, May 11, 2016 2:37 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] supply side connection - Tap connector 
recommendations

 

I don’t know about other parts of the country. 

 

If we have a self contained revenue meter – ie the type that cuts off power to 
the building when it is pulled, then we just pull it for any type of supply 
side connection or service upgrade. Sometimes we have to cut the utility 
locking mechanism (we have meter locking rings in our territory) in order to 
pull the meter. We don’t get the utility involved. 

 

If the project has a CT style meter where pulling the meter doesn’t cut off 
power, then we have to setup a disconnect reconnect with the utility for supply 
side connections. Screwing around in a live panel even with insulation piercing 
conductors is a risk that is not worth taking. The utility can supply a lot of 
current on the supply side of a service! 

 

-August

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to