Yah Drake, it can be done and I have done that before - in small main panels it involved a plastic shim under the neutral terminal block, and nylon nut/bolt to hold it down, with the EGC connected to GEC and GE on the main panel enclosure. With nice hard-wired small inverters available now (Morningstar SureSine) I don't think I'd ever mess with truck stop inverters wired to a main panel again. Or, just don't wire up the ground from the 120VAC outlet on the front of the portable inverter....that would work too. Ugh.
On Sun, Jun 12, 2016 at 11:46 AM, Drake < [email protected]> wrote: > You can isolate the neural bar and ground the equipment grounding system > to a grounding electrode. > > At 06:46 PM 6/11/2016, you wrote: > > Since you don't name the inverter OEM, I'm just guessing, but.....the > ground to neutral bond thing can indeed fry what I call "truck top" AKA > "portable" inverters. The puzzling thing in my experience is it can take 6 > months......1 month.....1 week......1 second for the failure. Or it might > work fine (but not be to code). > > My rule....to connect to a standard AC load panel (no matter how small) > the inverter has to have actual hard-wired AC Out terminals...hot, neutral > and ground. If the only way to connect it to the house AC system is a 120V > AC extension cord with the female end chopped off and hard wired to the > load panel, you are asking for trouble and have left NEC far behind. I got > well-zapped by one these in the past.... > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org