Remember if you do this you may have to implement a scheme to de energize the
other two if one goes offline. NEC dictates lines can't be unbalanced due to
the loss of an inverter. The rub is what does the utility require in terms of
allowable imbalance.
Typically it is around 6kW.
-----Original Message-----
From: "Howard Arey" <[email protected]>
Sent: 6/13/2016 14:11
To: "'RE-wrenches'" <[email protected]>
Subject: Re: [RE-wrenches] 20 kW 208/120 inverters
Consider using three single phase inverters putting out 208; one inverter for
AB leg, AC leg, and BC leg.
Howard “Scot” Arey
254-300-1228
[email protected] <mailto:[email protected]>
From: RE-wrenches [mailto:[email protected]] On Behalf
Of Carl Adams
Sent: Monday, June 13, 2016 1:09 PM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] 20 kW 208/120 inverters
Hello Wrenches,
I am looking of a recommendation on a 208 3 phase inverter in the 20 kW range.
Any suggestions?
Carl Adams
SunRock Solar
NABCEP Certified PV Installer