That's what the customer wanted, but even if I cut the leads short and terminated them, there would still be a risk of a ground fault to the module frame from water intrusion. In the end I was able to convince the customer to remove it. We moved a module from the end to the middle where this broken one was and cut off the excess rails. It looked just fine and they were happy.
I don't think I was very clear in my original post. The owner wanted to leave it physically in place but bypass it electrically. On Sat, Jul 23, 2016 at 4:14 PM, Chris Mason <[email protected]> wrote: > Why don't you bypass it but leave it in place? > > On Fri, Jul 22, 2016 at 7:26 AM, Jason Szumlanski < > [email protected]> wrote: > >> I came across shattered glass on an Evergreen PV module while doing a new >> homeowner system evaluation. My inclination is to remove the panel and >> bypass it, which would still leave the array well within the operating >> parameters for the inverter. However, the owner wants to just leave the >> panel physically in the array because it actually looks better that way, >> which I agree it does. You can hardly tell it's broken from ground level. >> >> I explained that there is a risk of a ground fault if the module is left >> physically in the array, but the owner who is pretty astute, mentioned that >> the fault voltage if a ground fault were to occur from that module would >> only be at 22.5V potential (he didn't mention the actual voltage, but he >> did correctly state that the maximum fault would be limited to the single >> module, which in this case is 22.5V @ 12A). While it may trip an inverter, >> it would probably not pose a safety risk. >> >> While he may be technically right, for now I have reused to do the work, >> but I told him I would think about it. >> >> Anyone been through this scenario? >> >> Jason Szumlanski >> >> >> >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: [email protected] >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/[email protected]/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> > > > -- > Chris Mason > NABCEP Certified Solar PV Installer™ > Solar Design Engineer > Generac Generators Industrial technician > > www.cometsolar.com <http://www.cometenergysystems.com> > 264.235.5670 > 869.662.5670 > Skype: netconcepts > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/[email protected]/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org