All,

 

The 2011 NEC reference for stand-alone systems is 705.12(D)(2) Exception:

 

Exception: Where the photovoltaic system has an energy storage device to allow 
stand-alone operation of loads, the value used in the calculation of bus or 
conductor loading shall be 125 percent of the rated utility-interactive current 
from the inverter instead of the rating of the overcurrent device between the 
inverter and the bus or conductor.

 

The 2014 NEC made this the rules of the road for all inverter output circuits 
connected to other sources.

 

Bill.

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Howie Michaelson
Sent: Friday, August 12, 2016 8:39 AM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] 120% rule for hybrid inverters

 

Mark,  I read that section as stating that both must be true, which I would 
take to mean if one is using a 20 amp breaker to protect the output from a 3 kW 
inverter, you need to count it as 20 amps toward the 120% rule, not the 15.63 
amps the 125% calculation would infer.  I know that 2014 was changed to allow 
for larger breakers to feed hybrid inverters, but I can't recite the code that 
allows that (unless I am misreading the intent of the section you quoted). Can 
you clarify this for me?

Thanks,

Howie




Howie Michaelson
NABCEP Certified Solar PV Installer™
Sun Catcher, LLC
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004

 

On Fri, Aug 12, 2016 at 9:39 AM, Mark Westbrock 
<[email protected] <mailto:[email protected]> > 
wrote:

Hi Mac,

 

The wording changed because in the 2011 NEC 705.12(D) you had to use the size 
of your backfeed breaker in calculating the busbar loading, but in 2014, 
705.12(D)(2)(3)(b) now says "125 percent of the inverter output circuit current 
and the rating of the OCPD protecting the busbar shall not exceed 120%".  

 

So, the 2014 wording basically allows all inverters to follow the exception 
that used to be there for hybrid inverters.  I hope that helps.

 

Cheers,

 

Mark




----

Mark Westbrock|  VP, Branch Manager |  Employee Owner

NABCEP™ Certified PV Installation Professional

NABCEP™ Certified 

Technical Sales Professional

NM EE98J Licensed Electrician

510 S. Main St., Las Cruces, NM 88001

cell  575.640.2432 <tel:575.640.2432>  |  office  575.524.2030 
<tel:575.524.2030> 

 <mailto:[email protected]> [email protected] 

 <http://www.positiveenergysolar.com/> www.PositiveEnergySolar.com

 

 <http://www.positiveenergysolar.com> 

 

 

On Fri, Aug 12, 2016 at 7:26 AM, Mac Lewis <[email protected] 
<mailto:[email protected]> > wrote:

Hello wrenches,

 

I am looking for the exception to the 120% rule in the 2014 code that allowed 
for compliance to the 120% rule to be based on the utility-interactive current 
as opposed to the backfeed breaker size for hybrid inverter.  I hope this still 
exists, but I'm having a hard time finding it in the 2014 code.  In 2011 it was 
705.12(D)2 Exception.  That was nice clear language that all inspectors 
accepted, I'm hoping the same exists for the 2014 code.

 

Thanks in advance code experts

 




 

-- 

 

 

 

Mac Lewis

"Yo solo sé que no sé nada." -Sócrates


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 



 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 



 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to