I’m curious. If a critical load center is powered from an alternative source and the main panel is not energized, won’t all neutral conductors still be energized from the sub panel back feeding the main? Or is that OK?
Larry On Sep 8, 2016, at 6:43 PM, Ray Walters <[email protected]> wrote: Hi Chris; Its the same as a switch leg for a light. The neutral stays at the light, only the hot is run down to the switch and back. Also, with some critical load panel set ups available (ie Generac), there is no provision to even run the neutrals to the new CLP. This is cleaner and involves much less splicing. Fewer connections is usually better in my book. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 9/8/2016 6:22 PM, Chris Mason wrote: > > I disagree with the response that you do not need to move the neutrals. You > should never have the load's phase wiring in one panel and the neutral in > another. > > > > > > Chris Mason > NABCEP Certified Solar PV Installer™ > Solar Design Engineer > Generac Generators Industrial technician > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org