Ron,
  I have used a 12v adapter plugged into the 120 AC from the generator to
the low voltage dc connection on the Magnum AGS unit to take care of the
negative continuity problem. Then a wireless connection of the two wire
start should work.




On Thu, Sep 22, 2016 at 8:31 PM, RM You <[email protected]> wrote:

> Hi Wrenches,
> I have a customer with a compromised underground wire from the Magnum AGS
> to his generator 150’ away. It quit working after 4 years. He’s wondering
> if there is another option to digging up the cable such as a wireless
> device. I’m thinking that the problem is the negative continuity between
> batteries which couldn’t be solved with a wireless device. Any suggestions
> appreciated!
>
> Ron Young
> earthRight Solar