Corey,

Generally, when choosing a larger system with multiple string inverters, the preferred architecture is to have the string inverters distributed - located at the ends of each row, and running AC lines back to a central AC combining location. This minimizes the length of the high voltage DC wiring to the short jump from the array to inverter and it allows short circuit/OCP for the runs back to the AC combiner to be provided by standard AC rated equipment. This also allows the wire runs to be standard building wire in plastic conduit.

Did you consider this and choose the "inverter wall" for some particular reason?

Mark Frye

Berkeley Solar Electric Systems

On 9/27/2016 1:50 PM, Corey Shalanski wrote:
Umm, is PV Wire rated for direct burial? I have seen several manufacturer spec sheets that suggest this is the case, but I haven't heard of anyone ever actually doing this.

Project Information:
1.6 MW single axis tracker
(35) 40 kW string inverters
Trenching from row ends to inverter wall, trench lengths will vary between 15-100 feet.

--
Corey Shalanski
Joule Energy
New Orleans, LA


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to