The Last large system I worked on we used direct burial alum 750s. We had a 
large crew out that day to help with that wire pull, it was 1000'. Eventually 
the backhoe that dug the trench was used to help pull the wires (slowly!). I 
guess I'd do it that way again but I don't have lots of  experience with large 
systems like others might. 

Jesse Dahl

NABCEP PV Installation Professional
IBEW Local 292 - Electrician 
Electrical/Solar PV Instructor - HCC

Sent from my iPhone

> On Sep 28, 2016, at 6:32 PM, Corey Shalanski <[email protected]> wrote:
> 
> We're in the process of designing our first >1MW system. It will include 
> inverter output combiner panels (potential aggregate current >700A) located 
> approx 100' from the system disconnects.
> 
> Since we have never previously dealt with wires this big (2 sets of 
> paralleled 500 mcm?) we are thinking that direct burial (aluminum) conductors 
> might be a good option - any suggestions? What wiring method do others use 
> for this type of large ampacity AC circuit? UF? USE? USE-2? Other?..
> 
> --
> Corey Shalanski
> Joule Energy
> New Orleans, LA
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to