Maverick:

Thanks for responding. You've been very helpful in the past with my battery based solution questions.

Daily load demand from the Protected Loads Panel is about 10kWh.

With 5 average daily peak sun hours, and 75% charging efficiency, the battery bank will receive about 13kWh of solar charging per day. The battery bank will be sized for 2 days of autonomy to 80% DoD (2 or 3 strings of 200RE batteries). A 6kW generator, which will be manually controlled, will provide charging assistance if the solar charging alone is not sufficient.

The 10kW (ac) SE inverter and associated 10.7kWp PV array, using the "Power Reduction Control" function, would be limited to about 3.5kW (ac).

Sizing the inverter and battery bank is not my issue - cranking back the output power of the SE grid-tied inverter is what I need help on.

The "standard" Outback GSLC solution uses one "Power Reduction Control" relay (100% to 0%). I want to use two Outback activated relays, and the SE inverter's "Power Reduction Control" function to:

(1) reduce the SE inverter power from 100% to 30% when the grid is down (relay #1)

(2) reduce the SE inverter power from 30% to 0% when the Radian wants to totally shut down the SE inverter (relay #2)

If this two-relay solution is possible, I do not have to kluge up a way to disconnect 70% of the PV array when the grid is down to keep the SE10000A-US inverter from overloading the 4kW Radian inverter and its battery bank.

Regards,

Gary Willett
Icarus Engineering / Solar Services LLC

On 10/18/16 9:23 AM, Maverick Brown wrote:
How many kWh are you shooting for?

 
On Oct 17, 2016, at 9:54 PM, Gary Willett <g...@icarussolarservices.com> wrote:

Esteemed Wrenches:

Anyone have experience setting up AC coupling with SolarEdge and the Outback Radian?

I have a client with a SolarEdge SE10000A-US inverter, equipped with 31 SunPower X21-345 modules (10.7kWp) and associated SolarEdge P400 DC optimizers. The DC optimizers are arranged into two strings of series connected optimizers: #1 = 16;  #2 = 15.

The client wants to add a limited battery backup solution, and a 4kW inverter will serve the needs of the requisite protected loads panel.

I am considering using the Outback Radian GS4048A inverter in conjunction with the GSLC175-AC-120/240 AC-Coupling Center.

I want to make a slight change to the PRI programming on the SolarEdge inverter, and add another relay contact to the Radian, to accommodate a 4kW Outback inverter AC coupled to a 10kW SolarEdge inverter.

This is my first AC coupling project with these systems. The analysis below is based solely on review of available documents on the Outback and SolarEdge web sites.

Any help or guidance will be greatly appreciated.

Regards,

Gary Willett
Icarus Engineering / Solar Services LLC

References:
(1) Outback Application Note "AC Coupling OutBack Power Radian Inverters with SolarEdge N. American Inverters"
http://www.outbackpower.com/downloads/documents/technotes/ac_coupling_tech_note.pdf

(2) Outback Application Note "Adding the battery back-up power option to existing grid-tied PV/solar systems"
http://www.outbackpower.com/downloads/documents/flexcoupled/app_note_acc_new.pdf

(3) SolarEdge Application Note "SolarEdge Inverters, Power Control Options"
http://www.solaredge.com/sites/default/files/application_note_power_control_configuration.pdf
REF (2); Page 9 of 14 - Outback's AC Coupling Guideline Number Two:
The OutBack inverter power rating should be 1.25% of the GT inverter power rating. This guideline ensures that the GT inverter does not overwhelm the charging circuitry in the OutBack inverter if the load demand goes to zero and all available GT inverter power is flowing to the OutBack inverter.

With the 4kW GS4048A inverter, the PV power rating is therefore limited to 3.2kW. This is 30% of the nameplate rating of the PV array (3.2/10.7).
REF (3); Page 4 of 5 - SolarEdge/OutBack Radian Wiring Diagram:
On the male connector that fits into the PRI connector on the SolarEdge PCB, two wires are connected from the OutBack GSLC load center 12V relay (OBR-16-DIN).
When activated, a normally open contact (NO) of the Outback OBR-16-DIN 12V relay supplies +5V from "pin 8" to "pin 6" of the SolarEdge inverter's "Power Reduction Interface (PRI) port".
REF (1); Page 3 of 5 - SolarEdge Setup / Programming:
Per the App Note, when the Radian wants to shut down the SolarEdge, the OBR-16-DIN 12V relay is activated and a "1" is applied to bit 1 of the PRI. This takes the SolarEdge output power, in a gradual manner, from 100% to 0%.
"DEFAULT" SolarEdge Programming
0000 <100,1,00,Y> ----meaning = 100% power, 1.00 power factor, point is active
0001 <0,1.00,Y> ----meaning = 0% power, 1.00 power factor, point is active
For my project, when the grid is down, the SolarEdge inverter must be limited to 30% power. I want to use the second NO/NC contact on the OBR-16-DIN 12V relay to accomplish this. Not yet sure exactly how to accomplish this in the Radian programming, but here's how I want it to function:
(a) when the grid is down, the second OBR contact, connected to bit 2 of the PRI, is activated and a "1" is applied to bit 2. This takes the SolarEdge output power, in a gradual manner, from 100% to 30%.

(b) when the Radian wants to shut down the SolarEdge, a "1" is applied to bit 1. This takes the SolarEdge output power, in a gradual manner, from 30% to 0%.
"PROPOSED" SolarEdge Programming
0000 <100,1,00,Y> ----meaning = 100% power, 1.00 power factor, point is active
0001 <0,1.00,Y> ----meaning = 0% power, 1.00 power factor, point is active
0010 <30,1.00,Y> ----meaning = 30% power, 1.00 power factor, point is active
0011 <0,1.00,Y> ----meaning = 0% power, 1.00 power factor, point is active
Is this doable?


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to