Great memory Allan! Thanks.

Ron

> On Oct 25, 2016, at 9:32 PM, Allan Sindelar <[email protected]> wrote:
> 
> Ron,
> Shooting from memory here... the T220 was rated at 2800 watts max, as 
> compared to the later T240, which is rated at 3900 watts continuous. At 240 
> VAC 2800W is just a bit over 10A. Given that use as a balancing 
> autotransformer for a generator is continuous duty, this capacity rating is 
> most likely due to how much heat it can tolerate. Given this the 15A fusing 
> seems quite appropriate and I wouldn't change it. 
> Allan
> 
> Allan Sindelar
> [email protected] <mailto:[email protected]>
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
>  
> On 10/25/2016 5:53 PM, RM You wrote:
>> Hi Wrenches, looking for help from someone who remembers the old T220 
>> Autotransformer from Trace. I have a used one and it came with built in 15a 
>> fuses which seem small. I’m wondering if the size of the transformer 
>> actually changed with the T240 subsequent version or if the 25a breakers in 
>> the T240 were just considered a more acceptable design component for the 
>> time. Bottom line is would it be advisable to change out the built in 15a 
>> for a higher rating to use this as a balancing transformer on 240v output 
>> from a generator.
>> 
>> Ron
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html 
>> <http://www.mail-archive.com/[email protected]/maillist.html>
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html 
> <http://www.mail-archive.com/[email protected]/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to