Can you come out of the line side tap to the
lugs, and connect the solar to the breaker
terminals? This way a retainer clip is not required.

At 11:12 AM 11/30/2016, you wrote:

Sorry I should have elaborated more from the beginning.

Â

I am using the panel as a service disconnect for
a lineside connection (can’t use a
fused/bladed disco because of space
constraints). Originally I bought a QO 70A
panel, but soon realized that the Square D
retention clip (PK2MB) is only compatible with
their larger panels. So I bought a larger panel
(100A 8 Circuit) and then received some feedback
that having the open spaces (even if labeled
that “Do Not Add Loads”) could raise a flag
with an inspector. So then I was back on the
hunt for a dedicated 2 Pole 60A or 70A panel
with a compatible retention clip for a 30A
breaker. Eaton’s retention options only start
in the 60A range (the smaller breakers don’t
have the hole in them to put the bolt through).
Square D said they don’t have an option for
their 70A panel. There aren’t any good Siemans
distributors near me but I wasn’t finding an
option via google for them either.

Â

I talked with another Wrencher on the phone and
received this feedback which I’m just going to
cut and paste to include it in this thread:


“The NEC doesn’t require a hold down clamp
for the circuit breaker unless it can be backfed
from a multi-mode or stand-alone inverter (690.10(E)).

The language implies that a hold-down is
therefore not required elsewhere. Most modern
breakers (def. QO’s) are not marked “line”
and “load” so no problem there (also in same code section).

Â

Even when it was a requirement for all PV
outputs, John Wiles had argued that taking off
the panel cover, which required a tool, served
as the hold-down, and this was generally accepted.”

Â

So taken that advice I’m back to using the QO
70A panel but without a retention clip (or
calling the lid the "retention clip").

Â

For what its worth I have passed inspections
prior using the retaining clip from a generator
interlock kit (QOCGK2C) on a QO 100A panel, but
felt like there must be a better option out there....

Adam Katzman
Autonomous Energies
PO Box 1245
Kingston, NY 12402
<http://www.autonomousenergies.com>www.autonomousenergies.com
(518) 567-1468


On Wed, Nov 30, 2016 at 10:45 AM, Drake
<<mailto:[email protected]>[email protected]>
wrote:
Siemens has main breaker retainers. The
retainers for QO seem work on some boxes and not
others. It doesn't work on 6 space boxes I've
purchased, but does work on the 8.

At 10:14 PM 11/29/2016, you wrote:

Wrenchers,

I’m trying to find a 60A 2 Pole Breaker Box
that hashas a compatible retaining clip. The QO
retaining clip (PK2MBCP) seems to only be
compatible with their 4-8 circuit load centers. What are my options? Thanks!

Thanks

Adam
_______________________________________________
List sponsored by Redwood Alliance

List Address:
<mailto:[email protected]>[email protected]

Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html


List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<http://www.members.re-wrenches.org/>www.members.re-wrenches.org



----------
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
Avast logo
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>


This email has been checked for viruses by Avast antivirus software.
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>www.avast.com



_______________________________________________
List sponsored by Redwood Alliance

List Address:
<mailto:[email protected]>[email protected]

Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to