Also, you didn't specify, but AC and DC are specifically allowed in the same raceway per 300.3(C)(1). Only If the DC circuits are PV source or output circuits, then 690.31(B) prevails, which says they can't share a raceway. But again, as Chris mentions, this restriction does not apply to direct burial.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 12/28/2016 12:58 PM, Chris Mason wrote:
No problem with same trench, the requirements are that they are not in the same raceway.

On Wed, Dec 28, 2016 at 1:37 PM, Corey Shalanski <co...@joule-energy.com <mailto:co...@joule-energy.com>> wrote:

    For some upcoming utility-scale projects our design team is
    wondering about placing direct-bury AC and DC circuits in the same
    trench.
    - Firstly, is this even /Code/-permissible?
    - Secondly, are there any common sense reasons (induced
    voltage/signal interference/etc) for not doing this?

    Thanks,
    Corey Shalanski
    Joule Energy
    New Orleans, LA

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





--
Chris Mason
NABCEP Certified Solar PV Installerâ„¢
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to