Recently we were asked to do a combined inspection and engineering review of a 
362.70 kWdc PV system using 5 Sungrow SG60KM-U inverters. We found issues like 
palm trees and air handling equipment shading significant parts of the arrays, 
electrician’s tape and palm fronds on the surface of the modules. But we also 
observed two significant Code violations: PV  source conductors lying on the 
surface of the torch-down roof and lack of bushings at the connectors on the 
ends of 2” LFMC. The PV source conductors got secured and we saw bushings 
threaded onto the ends LFMC connectors.

Upon close inspection we discovered that the bushings had been broken at one 
point on their circumference, no doubt to simplify their attachment. Their were 
11 PV source circuits (22 current-carrying 10 AWG PV Wire conductors.)

Is this a NEC Code violation? If so, what section would we cite? It seems 
obvious that the bushing had been “modified”, but I would like to be more 
specific. Or does it come under the workmanship category?

Regards,

- Peter Parrish

Peter T. Parrish, Ph.D., President
SolarGnosis
1107 Fair Oaks Ave.
Suite 351
South Pasadena, CA 91030
(323) 839-6108
peter.parr...@solargnosis.com
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to