I talked to SMA tech support. They said the 5.0
and 6.0 models were compatible with AC coupling.
AEE supplied the SI 485PB NR Piggyback card with RJ 45 cable.

At 06:45 AM 3/10/2017, you wrote:
Well my supplier was not aware of any additional
part# for this purpose. Nor was their anything
in their manual stating compatibility.
Part# PLEASE, It does seem short sighted of the
company who pioneered AC Coupling to no longer
provide us w/ equipment for said ACC.
On Mar 9, 2017, at 8:47 AM, Drake
<<mailto:[email protected]>[email protected]>
wrote:

I was told by SMA tech support that the new SMA
US 40s were compatible with AC coupling. I was
provided with interface cards for the purpose.

At 04:21 PM 3/8/2017, William Miller wrote:

What are the limitations of the new SMA inverters?

Drake


Wrenches:
Â
As a caution:Â  The TL22 inverters have been
discontinued.  The TL40s have some
limitations as compared to the TL22s, in my
opinion.  You may still find TL22s on the shelf.
Â
William
Â
Â
<28a7dc11.jpg>
Lic 773985
<http://www.millersolar.com/>millersolar.com
805-438-5600
Â
From: RE-wrenches [
mailto:[email protected]] On Behalf Of Tump
Sent: Wednesday, March 08, 2017 1:13 PM
To: <mailto:[email protected]>[email protected]; RE-wrenches
Subject: Re: [RE-wrenches] Aquion Batteries
Â
I have dual Sunny Islands & dual SB 4000TL22US
 w/ 20 stack on one and another site w/ theÂ
Aspen 48MÂ w/ Schneider. I will say this; cost
per amp hour of storage  sucks w/ the Aquion
batteries. Both my client and I feel, that the
batteries, despite there size have very little
capacity. The “30”%DOD, that I have the
SIs set to start the Gen set, charges the
stacks OK but one gets better performance from
 charging w/slower solar source. The Aspen48M
is ~ 42X28X42” @563 AH of capacity, UnigyII
2000 Ah ~ 42x40x6’ tall. Batteries are
defiantly temperature sensitive, operating
should be ~ 60*. The set up w/ the SMA
product, adds additional cost due to the
required  BM200 AND  the Sunny Island
Interface Device, and the SM100 unless you are
buying theAspen48M which comes pre wired.
(Aspen 48M which comes thru w/ the sensing
module installed).  It is quite helpful, if
this is an off grid install due to the fact
that the BM200 needs and when things go south
Aquion can toggle the unit off site and help
w/ configuration &Â upgrades, to be connected
to the internet. This install also needs the
correct firmware to be installed on the SI
which when  was delivered, the firmware Â
would only load into the master then shut down
the system. Had to reconfigure as 2 separate
units, load the firm ware and then reconfigure for 2 phase.Â
I have spoken to the manufacture re/ lack of
capacity and was told that must be my loads…. NOT.Â
>I would suggest that despite their hype
these are quite expensive and require quite a
bit more of labor IF you are wiring the un
sensed stacks. And there is definitely a
learning curve if you are using the SI.
My own system and what I prefer to push IS the
SMA SI w/ the SMA SBs (make sure that you get
the TL22s as the newest SB is not compatible
for “ AC coupling” in this configuration)
w/ the Unigy II/MK line. (same battery) These
have buss bars, stack vertically , the
interlocking stacks is perfect for earthquake
locations. AND are totally recyclable.
Pictures  of the SMA install & insights of
battery installation available, contact me off line.  TUMPÂ
 Â
On Mar 8, 2017, at 12:55 PM, Martin Herzfeld
<<mailto:[email protected]>[email protected] > wrote:
Â
Has anyone worked with them with a Sunny
Island?  Space is not an issue for this client.
Martin Herzfeld, IREC Certified Master Trainer
™ for PV Installation Professional #IREC 10037
California Solaar Contractor License  #00833782  C46, D56, D31, C-7
Solar, Trenching, Pole Installation & Maintenance, Instrumentation
UL Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #C0068034
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
Registered NABCEP Continuing Education (CE) Provider
   Â
Â
On Jul 20, 2016 2:00 PM, "Jerry Shafer"
<<mailto:[email protected]>[email protected] > wrote:
We had a customer request them but once we
found out how many it would take, he decided
on the deka unigee instead. l dont like
running my OB's at such a low voltage as they
seem to get hotter due to the higher current.
Some of our other product lines don't even
reccomend aquions due to that low voltage,
suggest asking your inverter manufacture too.
Â
On Jul 20, 2016 10:52 AM, "Drake"
<<mailto:[email protected]>
[email protected]> wrote:
Hello Wrenches,
I have a client who is going to take the
plunge and buy a set of Aquion Batteries. They
look pretty good on paper, but I'm not sure
how well an inverter would function at the 40
V minimum. Does anyone have experience to
recommend them or warn against using them?
Thanks,
Drake
Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
<tel:740-448-7328>740-448-7328
<http://athens-electric.com/>http://athens-electric.com/
Â
_______________________________________________
List sponsored by Redwood Alliance
List Address:
<mailto:[email protected]>[email protected]
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
<http://www.members.re-wrenches.org/>www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance
List Address:
<mailto:[email protected]>[email protected]
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
<http://www.members.re-wrenches.org/>www.members.re-wrenches.org
Â
_______________________________________________
List sponsored by Redwood Alliance
List Address:
<mailto:[email protected]>[email protected]
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
<http://www.members.re-wrenches.org/>www.members.re-wrenches.org

Â
<blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>[email protected]Â
             Â
<blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>www.SWNL.net

                Solarwinds Northernlights      Â
       Serving Mid Coast Maine & Northern California
                        Â
207-832-7574Â Â Â Cl. 610-517-8401Â Â Â Â Â Â
                       Â
                              Blair "TUMP" May
               ********  MAINE'S CHARTER ********
                   Â
  NABCEP    "Certified PV Installer"Â
  Â
              ********  MAINE'S CHARTER ********
                  Trace
Xantrex "Certified" Dealer / Installer"
Â

Â
Â
Content-Type: image/jpeg; name="image003.jpg"
Content-Disposition: inline; filename="image003.jpg"
Content-ID: <[email protected]>
X-Attachment-Id: d32b0196b0d3a567_0.1


_______________________________________________
List sponsored by Redwood Alliance

List Address:
<mailto:[email protected]>[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



----------
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
Avast logo
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>


This email has been checked for viruses by Avast antivirus software.
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>www.avast.com


_______________________________________________
List sponsored by Redwood Alliance

List Address:
<mailto:[email protected]>[email protected]

Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

<blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>[email protected]
www.SWNL.net
                Solarwinds Northernlights
       Serving Mid Coast Maine & Northern California
                         207-832-7574   Cl.
610-517-8401
                              Blair "TUMP" May

               ********  MAINE'S CHARTER ********
                      NABCEP    "Certified PV Installer"

              ********  MAINE'S CHARTER ********
                  Trace Xantrex "Certified" Dealer / Installer"


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to