Short answer is yes, 2 days of autonomy should be fine. I am presently 
operating our off rid PV/hydro system at well under two days of autonomy.

 

I just crunched some numbers for our situation here in Vermont. Off grid system 
that is now 4.3kW PV and with a Harris micro-hydro turbine that I run at 325 
Watts.

·         24v system initially installed 30 years ago and with PV and inverters 
(dual OutBack) upgraded 7 years ago.

·         Present Battery bank now over 13 years old, 2v industrial flooded 
LA's rated at 1200 AH. Originally designed for 3+ days of autonomy.

·         Our large home has been a true two family home for the past three 
years, with a full second kitchen along with TV etc. we are now using about 
15kWh/day during the winter. Our Tarm wood gasification, forced hot water 
heating system uses quite a bit of electricity but we can heat the whole deal 
without burning any oil, or propane, for this 4,000 sq foot two family home in 
northern Vermont it is well worth it. We harvest the 10 cords of hardwood out 
of our woods.

·         28,880Wh battery bank / 15,000 Wh = 1.5 days of autonomy. I didn't 
know how well this would work when we added the second living space with the 9 
yr old batteries at that point. But I have not had to change a thing.

·         I have my next set of batteries (sized them a little larger, 1350AH) 
waiting in reserve in my basement (properly cared for per Surrette/Rolls 
instructions) as I don't know when the present 13 yr + set will fall off the 
cliff. I'm watching them closely, no alarming signs of the end yet. Monitoring 
all cell post terminals with my handheld IR thermometer when battery bank is 
charging hard and or when the system is under a large load. So far all 
terminals get up to 86 degrees F at most. Water use has not changed much at all 
yet and specific gravity readings are all very good.

·         More numbers: The charge rate with 4.3k of PV only is about a C/8 on 
the battery bank. 

·         Hydro is 325W, run 24/7 from late October through April, then as 
needed during rainy periods. 

·         Diesel Gen set charges at 160 Amps, so during the cloudy, snowy 
winter periods the hydro and gen combined charge at about a C/7 rate. 

Dave

 

David Palumbo 

Independent Power LLC

462 Solar Way Drive

Hyde Park, VT 05655

802-371-8678 cell

802-888-4917 home

 

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Matt Sherald
Sent: Wednesday, April 26, 2017 7:21 AM
To: RE-wrenches
Subject: [RE-wrenches] Hydro Off-grid Battery Sizing

 

Good morning!  I went to bed wondering if the off-grid battery bank sizing 
rules that I use for PV systems hold true for hydro-based systems.  I woke up 
and I was still mulling this over.

My battery bank sizing standard is to use the method outlined in the SEI 
Photovoltaics Manual.  I would presume that since the charging source is fairly 
consistent (day-to-day and hour-to-hour) that I could then reduce the days of 
autonomy to 2-days.  

I'm curious though if anyone has advice for sizing a battery bank for hydro.  
Any suggestions would be greatly appreciated.


 

Thank you!

-- 

Matt Sherald

PIMBY Energy, LLC

NABCEP Certified Solar PV Installer®

304-704-5943

www.getpimby.blogspot.com
www.getpimby.com

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings: